anybody have tried connecting an s7 300 plc 315-2DP as master and an S7 200 (with profibus interface) profibus connection.?
ill will have an hmi connected to mpi to the 315 cpu and s7 200 connected as slave to the 315 using the profibus connection.
is it possible to control all the input and output of the s7 200 using this kind of connection?
is there any SFB needed to be loaded
Thanks to all>>>>>
marcs7
Posts: 52 Joined: Fri Jun 08, 2007 4:00 pm
Location: Europe
Post
by marcs7 » Thu Feb 12, 2009 11:19 am
the EM277 make a I/O virtual in the V memory.
you master write the ouput and read the input, the input and the output gone in the V memory.
tips
here
if you configure the slave in consistency area dont forget the SFC15 SFC14.
ivan_euler
Posts: 12 Joined: Wed Feb 04, 2009 2:51 am
Location: phillippines
Post
by ivan_euler » Thu Feb 12, 2009 11:05 pm
this means that ill configure the s7 200 as EM then ican used simatic manager to prog ram the S7-200 dirctly using the 315 as master. Is that wat u mean?
Thanks
Umencho
Posts: 508 Joined: Mon Jul 16, 2007 12:28 pm
Location: Europe
Post
by Umencho » Fri Feb 13, 2009 4:41 am
Hello
Look at How can you communicate data between the S7-200 and the S7-300 via PROFIBUS DP?
FAQ
http://support.automation.siemens.com/W ... en/2615830
I hope this will answer to your questions.
regards