[?]: Using Analog Input 2 wire 0-20mA...?
hand_drake
Post by hand_drake »
Hello everybody... :o
How we can use analog input 2 wire but the transmitter is 2 wire...? :roll:
Hence, the analog 2 wire of Siemens Step7 (All analog input module) is 4-20 mA, without changing the transmiter, because the transmitter is 0-20mA.
Thanks for answer.
dsekulic
Post by dsekulic »
Are You sure that transmitter is 2 wire because transmitter power supply is provide over this 2 wires. That's why 2 wire transmitters have no possibilities to choose 0..20mA range.
regards
hand_drake
Yes, i am sure about this input analog. The input that i obtain is from a feedback control valve 0..100% = 0..20 mA. It's quite strange, but it's true.
charles_ch_tan
Post by charles_ch_tan »
2 Wires transmitter, 1 wire for 24VDC whereby another 1 is for Signal (I+).
If your feedback control valve 0..100% = 0..20 mA.
Then in Simatic Manager Hardware Configuration, you might set the Alalog Input from 4-20mA to 0-20mA. Remembered the Jumper Setting at that Analog Input Module Cards it self must set correctly.
dsekulic
Post by dsekulic »
Do You have link or model of control valve You mentioned?
regards
hand_drake
Ok....
Finally, i make nothing different with the program, but i recalibrated the valve. Using 2 wire analog input there is no 0-20mA, only 4-20mA.
Calibration the valve:
4mA=0% opening feedback
20mA=100% opening feedback
And it works.