One 4-20mA signal to two analog inputs
MZohaib92
Post by MZohaib92 »
I want to read transducer signal on PLC.
I am using 7kg60008ab/nn transducer and it's analog (4-20mA) output is connected with analog meter.
Can I connect the transducer current output (4-20mA) signal to PLC analog input in series with analog meter display???
So that I can read the value on PLC simultaneously with analog meter?
Re: One 4-20mA signal to two analog inputs
Only via Analog module with Differential input without connected Ground in "4-wire configuration"
https://support.industry.siemens.com/cs ... 6hb00-0da1
(sdoc) https://support.industry.siemens.com/cs ... ti=0&dl=en
georg_demmler
Post by georg_demmler »
my first question, it is correct that the output signal is 4-20mA?
I found in one manual 0-20mA. But I don't understand the differce between NN and MM.
The transducer has 3 analoge output signals.
My advise ist to test something with two analog meters in out line with the output like following:
output -- analog meter --analog meter -- output
Hope it helps
h4rdw4re
Post by h4rdw4re »
Or, easiest way, you can use signal conditioner/splitter.
One input multiple output.
You can choose loop powered device or active device.
There is option with screw or push in.
One example:
loop powered with screw connection
https://catalog.weidmueller.com/procat/ ... ge=Product
active power with screw connection
Or all in one...
Or cheapest option as georg_demmler said. Configure other outputs and use it for analog meter.
Cheers.