I know that most PLC inputs are 24vdc,
but what would happen to the PLC if you applied 24vac to the inputs if it was a dc input?
[?]: 24vac PLC inputs ?
misa1515
Re: PLC inputs
24VAC on 24VDC input - value in PLC will flicker on 0 and 1
Jbeard
Re: PLC inputs
So that could be why we have alot of problems with these air handlers that are wired this way. The manufacturer says we don't know what where talking about.
Re: [?]: 24vac PLC inputs ?
1. SIMATIC ET 200SP, digital input module, DI 8x 24 V AC...48 V UC
https://support.industry.siemens.com/cs ... 6cf00-0au0
6ES7131-6CF00-0AU0
ET 200SP, DI 8x 24VAC..48VUC BA, PU 1
https://support.industry.siemens.com/cs ... /109759596
2. use buffer relay, 24vac LZX:PT570524
https://support.industry.siemens.com/cs ... 3Apt570524
6ES7131-6CF00-0AU0