Does anybody work with GE Fanuc PLCs?
I configured hardware and exceed backplane bus current by 10 mA (high limit for PS module IC200PWR002/012 is 1500mA and I have 1510 mA). Is it critical?
I tryed configure second power supply module (IC200PWB001 PS Booster Carrier + IC200PWR001/011 PS module). After configuration validating, main PS module power consumption is 1510 mA and booster PS is 0 mA. And there is the same error message.
Can I use additional power supply in this case?
Spoiler
________________________________________
Report Name: Hardware Configuration
Target Name: TestPLC
Report Time: 06.04.2015 14:20:34
1 Overview
2 Main Rack: IC200CPUE05, VersaMax Rack System
+5.0 Voltage (Amps) : +3.3 Voltage (Amps) :
Used 0.860 0.650
Supplied 0.850 1.000
Used 0.000 0.000
Supplied 1.500 0.250
3 Detailed View
4 Main Rack: Slot 0
5 IC200PWR002/012 Isolated (012) 24VDC Expanded 3.3 VDC Input Power Supply
6 Power Consumption
Voltages / Supplied
+5.0 Voltage (Amps) : 1.50
+3.3 Voltage (Amps) : 1.00
7 Main Rack: Slot 0
8 IC200CPUE05 CPU W/ENET Cfg User Memory Port 1 RS232 Port 2 RS485
9 Settings
Parameters / Values
I/O Scan-Stop: No
Power Up Mode: Run
Logic / Configuration From: RAM
Registers: RAM
Passwords: Enabled
Checksum Words: 8
Default Modem Turnaround Time (.01 Sec/Count): 0
Default Idle Time (Sec): 10
SFC Timer Faults: Disabled
SNP ID:
Switch Run / Stop: Enabled
Switch Memory Protect: Disabled
Diagnostics: Enabled
Fatal Fault Override: Disabled
EZ Program Store: RAM Only
10 Scan
Parameters / Values
Sweep Mode: Normal
Sweep Timer (mSec): N/A
11 Port 1 (RS-232)
Parameters / Values
Port Mode: SNP
Port Type: Slave
Data Rate (bps): 19200
Parity: Odd
Stop Bits: 1
Timeout: Long
Turnaround Delay (mSec in 10 mSec Increments): 0
SNP ID:
12 Port 2 (RS-485)
Parameters / Values
Port Mode: SNP
Port Type: Slave
Parity: Odd
Stop Bits: 1
Timeout: Long
SNP ID:
Converter Power Consumption (Amps) : 0
13 Memory
Parameters / Values
%I Discrete Input: 2048
%Q Discrete Output: 2048
%S System Use: 128
%M Internal Use: 1024
%T Temporary Status: 256
%G Genius® Global: 1280
%AI Analog Input: 128
%AQ Analog Output: 128
%R Register Memory: 2048
14 Ethernet
Parameters / Values
Configuration Mode: TCP/IP
IP Address: 192.168.0.50
Subnet Mask: 255.255.255.0
Gateway IP Address: 0.0.0.0
Status Address: %I00257
Status Length: 80
NTP Time Server #1 IP Address 0.0.0.0
NTP Time Server #2 IP Address 0.0.0.0
NTP Time Server #3 IP Address 0.0.0.0
15 Local Station Manager
Parameters / Values
Data Rate (bps): 9600
Flow Control: None
Parity: None
16 Power Consumption
Parameters / Values
+5.0 Voltage (Amps) : 0.160
+3.3 Voltage (Amps) : 0.650
17 Main Rack: Slot 1 IC200CHS022 I/O Carrier Box Style - Vertical
18 IC200ALG230 Analog Input 12 Bit Volt/Curr 4Ch
19 Settings
Parameters / Values
Reference Address: %AI0001
Length: 4
20 Module Parameters
Parameters / Values
%AI Default / Hold Last State: Default
Report Faults: Enabled
Operation Mode: Bipolar
21 Input Parameters
Channel / Default Value
1 0
2 0
3 0
4 0
22 Wiring
Terminal / Wiring Information
From Terminal A1 to Terminal B18 : No wiring information.
23 Power Consumption
Parameters / Values
+5VDC (Amps): 0.125
24 Main Rack: Slot 2 IC200CHS022 I/O Carrier Box Style - Vertical
25 IC200ALG230 Analog Input 12 Bit Volt/Curr 4Ch
26 Settings
Parameters / Values
Reference Address: %AI0005
Length: 4
27 Module Parameters
Parameters / Values
Operation Mode: Current (4 - 20mA)
28 Input Parameters
1 0
2 0
3 0
4 0
29 Wiring
30 Power Consumption
Parameters / Values
+5VDC (Amps): 0.125
31 Main Rack: Slot 3 IC200CHS022 I/O Carrier Box Style - Vertical
32 IC200ALG230 Analog Input 12 Bit Volt/Curr 4Ch
33 Settings
Parameters / Values
Reference Address: %AI0009
Length: 4
34 Module Parameters
Parameters / Values
35 Input Parameters
1 0
2 0
3 0
4 0
36 Wiring
37 Power Consumption
Parameters / Values
+5VDC (Amps): 0.125
38 Main Rack: Slot 4 IC200CHS022 I/O Carrier Box Style - Vertical
39 IC200ALG230 Analog Input 12 Bit Volt/Curr 4Ch
40 Settings
Parameters / Values
Reference Address: %AI0013
Length: 4
41 Module Parameters
Parameters / Values
42 Input Parameters
1 0
2 0
3 0
4 0
43 Wiring
44 Power Consumption
Parameters / Values
+5VDC (Amps): 0.125
45 Main Rack: Slot 5 IC200CHS022 I/O Carrier Box Style - Vertical
46 IC200MDD842 Mixed 24VDC Pos/Neg Logic In Grp 16Pt / Out 24VDC Pos 0.5A ESCP 16Pt
47 Settings
Parameters / Values
Reference Address: %I00001
Length: 16
Reference Address: %Q00001
Length: 16
48 Module Parameters
Parameters / Values
DC Filter Select: 1 mSec
%I Default / Hold Last State: Default
%Q Default / Hold Last State: Default
49 Input Parameters
Point / Default Value
1 0
2 0
3 0
4 0
5 0
6 0
7 0
8 0
9 0
10 0
11 0
12 0
13 0
14 0
15 0
16 0
50 Output Parameters
1 0
2 0
3 0
4 0
5 0
6 0
7 0
8 0
9 0
10 0
11 0
12 0
13 0
14 0
15 0
16 0
51 Wiring
52 Power Consumption
Parameters / Values
+5.0 Voltage (Amps) : 0.100
53 Main Rack: Slot 6 IC200CHS022 I/O Carrier Box Style - Vertical
54 IC200ALG320 Analog Output 12 Bit Curr 4Ch
55 Settings
Parameters / Values
Reference Address: %AQ0001
Length: 4
56 Module Parameters
Parameters / Values
%AQ Default / Hold Last State: Hold Last State
57 Output Parameters
1 0
2 0
3 0
4 0
58 Wiring
59 Power Consumption
Parameters / Values
+5VDC (Amps): 0.050
60 Main Rack: Slot 7 IC200CHS022 I/O Carrier Box Style - Vertical
61 IC200ALG320 Analog Output 12 Bit Curr 4Ch
62 Settings
Parameters / Values
Reference Address: %AQ0005
Length: 4
63 Module Parameters
Parameters / Values
64 Output Parameters
1 0
2 0
3 0
4 0
65 Wiring
66 Power Consumption
Parameters / Values
+5VDC (Amps): 0.050
67 Main Rack: IC200PWB001 Power Supply Booster Carrier
68 IC200PWR001/011 Isolated (011) 24VDC Input Power Supply
69 Power Consumption
Voltages / Supplied
+3.3 Voltage (Amps) : 0.25
70 Reference Details
71 %AI References
Overlap Start End Addr Mem Type Cat Num
1 4 (0.1) Consumed IC200ALG230
5 8 (0.2) Consumed IC200ALG230
9 12 (0.3) Consumed IC200ALG230
13 16 (0.4) Consumed IC200ALG230
Total %AI: 16 Highest Reference: 16
72 %AQ References
1 4 (0.6) Produced IC200ALG320
5 8 (0.7) Produced IC200ALG320
Total %AQ: 8 Highest Reference: 8
73 %I References
1 16 (0.5) Consumed IC200MDD842
257 336 (0.0) Consumed IC200CPUE05
Total %I: 96 Highest Reference: 336
74 %Q References
1 16 (0.5) Produced IC200MDD842
Total %Q: 16 Highest Reference: 16
1 Overview
Used 0.860 0.650
Used 0.000 0.000
3 Detailed View
4 Main Rack: Slot 0
6 Power Consumption
Voltages / Supplied
7 Main Rack: Slot 0
9 Settings
Parameters / Values
I/O Scan-Stop: No
Power Up Mode: Run
Registers: RAM
Passwords: Enabled
Checksum Words: 8
SNP ID:
10 Scan
Parameters / Values
Sweep Mode: Normal
11 Port 1 (RS-232)
Parameters / Values
Port Mode: SNP
Port Type: Slave
Parity: Odd
Stop Bits: 1
Timeout: Long
SNP ID:
12 Port 2 (RS-485)
Parameters / Values
Port Mode: SNP
Port Type: Slave
Parity: Odd
Stop Bits: 1
Timeout: Long
SNP ID:
13 Memory
Parameters / Values
%S System Use: 128
14 Ethernet
Parameters / Values
Status Length: 80
Parameters / Values
Flow Control: None
Parity: None
Parameters / Values
19 Settings
Parameters / Values
Length: 4
Parameters / Values
21 Input Parameters
1 0
2 0
3 0
4 0
22 Wiring
Parameters / Values
+5VDC (Amps): 0.125
26 Settings
Parameters / Values
Length: 4
Parameters / Values
28 Input Parameters
1 0
2 0
3 0
4 0
29 Wiring
Parameters / Values
+5VDC (Amps): 0.125
33 Settings
Parameters / Values
Length: 4
Parameters / Values
35 Input Parameters
1 0
2 0
3 0
4 0
36 Wiring
Parameters / Values
+5VDC (Amps): 0.125
40 Settings
Parameters / Values
Length: 4
Parameters / Values
42 Input Parameters
1 0
2 0
3 0
4 0
43 Wiring
Parameters / Values
+5VDC (Amps): 0.125
47 Settings
Parameters / Values
Length: 16
Length: 16
Parameters / Values
49 Input Parameters
1 0
2 0
3 0
4 0
5 0
6 0
7 0
8 0
9 0
10 0
11 0
12 0
13 0
14 0
15 0
16 0
1 0
2 0
3 0
4 0
5 0
6 0
7 0
8 0
9 0
10 0
11 0
12 0
13 0
14 0
15 0
16 0
51 Wiring
Parameters / Values
55 Settings
Parameters / Values
Length: 4
Parameters / Values
1 0
2 0
3 0
4 0
58 Wiring
Parameters / Values
+5VDC (Amps): 0.050
62 Settings
Parameters / Values
Length: 4
Parameters / Values
1 0
2 0
3 0
4 0
65 Wiring
Parameters / Values
+5VDC (Amps): 0.050
Voltages / Supplied
71 %AI References
72 %AQ References
73 %I References
74 %Q References