A set bit in FC
azad_azida
A set bit in FC
Post by azad_azida »
Hi All,
I am working on a FC for a shut of valve and Star Delta Motor which later have a Set bit inside.
The FC later to be called in many parts of program. The Set bit is for Alarm/Trip signal to show the valve or motor is faulty.
The FC is called at few places, later i have update it for some reason, the Set bit become crazy where it ON and OFF once my FC is activated.
If the Set bit is changed with other bit, then it is OK. Once i put back the original bit, it goes crazy.
Is there any explanation? how can i fix the original bit?
Thanks.
SHKODRAN
Re: A set bit in FC
Post by SHKODRAN »
Can you post a few lines of code, maybe someone can help you better about what you want to do.
Regards.
azad_azida
Re: A set bit in FC
Here it is, i write in LAD and good in STL. M5.2 is Clock pulse.
A     #Activate
      AN    #Valve_Trip
      =     #Valve_Close
      A(
      A     #Valve_Close
      A     #Close_Lim
      AN    #Open_Lim
      O
      AN    #Valve_Close
      A     #Open_Lim
      AN    #Close_Lim
      JNB   _003
      L     0
      T     #Trip_Counter
      SET
      SAVE
      CLR
_003: A     BR
      JC    trp
 A(
      A     #Valve_Close
      A(
      ON    #Close_Lim
      O     #Open_Lim
      O
      AN    #Valve_Close
      A(
      ON    #Open_Lim
      O     #Close_Lim
      A(
      L     #Trip_Counter
      L     10
      >=I
      S     #Valve_Trip
      AN    #Valve_Trip
      A     M      5.2
      JNB   _004
      L     #Trip_Counter
      L     1
      +I
      T     #Trip_Counter
_004: NOP   0
 JU    trp2
trp:  A     #Trip_Reset
      R     #Valve_Trip
    AN    #Valve_Close
      JNB   _005
      L     0
      T     #Trip_Counter
_005: NOP   0
trp2: A     #Close_Lim
      =     #Valve_Close_Visu
almaz78
Re: A set bit in FC
Post by almaz78 »
without looking at your code.
Probably its because you are using temp variables in FC for variables that need to retain their condition for next scan (static area in FB)? but i could be wrong
SHKODRAN
Re: A set bit in FC
Post by SHKODRAN »
Hi ,
it's not so much clear , please , can you post your fc in the project or library?
Thanks.
azad_azida
Re: A set bit in FC
Hi Shkodran,
Sorry i am late as i am travelling.
Here is the link for the project.
http://www.datafilehost.com/d/9b9f7264
Hi Almaz, tq for your reply but i don't want to use a FB since it will have a DB for every call.
Every shut of valve i use will create a DB.
SHKODRAN
Re: A set bit in FC
Post by SHKODRAN »
Hello ,
I have made some change on your code.
Let me know if you understand what I have done.
Regards,
https://dl.dropboxusercontent.com/u/36112245/Test_fc.zip