freeze a signal ( DI or DO) from graphics push button
другие контроллеры
azgor_03
Post by azgor_03 »
Can i do freeze a signal ( DI or DO) from graphics push button directly to controller hardware.
So that i can avoid hardware push button.
In that case which push button need to use. using control builder M professional 800xA 5.1 version.
Linkinx64
Re: freeze a signal ( DI or DO) from graphics push button
Post by Linkinx64 »
This is called "Forced". Available from the faceplate of standard function blocks (in SignalLib library).
azgor_03
Post by azgor_03 »
ple send the procudure
azgor_03
Post by azgor_03 »
Suppose i have a selector switch to give a selection like local mode selection. by using the selector switch if i on/off the switch then it make true or false the hardware input.
now how can i do this by process graphics -2. need procudure
Linkinx64
Post by Linkinx64 »
What kind of procedure should be? This switch is located right on the object faceplate - buttons Set/Reset Force state.
When you click "Set Force" from (e.g.) SignalInBool faceplate the last channel value (from "In" IO) will be copied to the "Out" output and buttons "Activate"/"Deactivate" will be enabled for the operator intervention to the process. Further changes of the IOValue in "Forced" mode will be omitted.
However, if you need to set the "Manual" mode from a logical input the "SignalInBool" block is not suitable for this.
Then it better to make your own functional block that provides "manual mode" activation from the logic or check for the library solutions (such as Pulp & Paper library).
But as you said
azgor_03 wrote:an i do freeze a signal ( DI or DO) from graphics push button directly to controller hardware.
it is assuming you need the "force" mode.
The manual mode is not directly controls the IO - it is rely on the process and safety interlocks and thus it is not always send/receive an operator-entered value to/from the logic/channel.