Dear All
I need to read 2 wires analog input 4-20 mA signal in S7 SIMATIC Manager OB1
1- I bring analog input module and put the selector to D position.
2-Connect the module in rack and the address in HW config. start with 272.
3-connect a 20 pin front connector and connect screw 1 to 24 VDC (external power supply) and screw 20 to GND (from the same external power supply and from the rack power supply "307") this mean I make a major ground for the system.
4-I connect the input to the screws 2 "+" and 3 "-" (this input taken from analog output module in another PLC)
5-I wrote a network in OB1 just MOV instruction to move PIW 272 to MW100
but the result is 7FFF "Hex" when I try to read signal from module (by right click the module in HW config. and select Monitor/ Modify the result also is 7FFF "Hex" I replace the module the result still the same.
What can I do?????????????????????
Thanks a lot.
[?]: Siemens S7 300 analog input 4-20 mA signal
omar zedan
dibolo
Re: [?]: Siemens S7 300 analog input 4-20 mA signal
make a variable table,put the mw there and then you can make it to dec
Lepes9
Check the diagnostic list of the module, something is wrong (wire break, overflow etc.). (HW-congfig, highlight module, CTRL-D for diagnosis)
Greets
Lepes9
Greets
Lepes9
Yury
You parameterized input in the HW config as a 2-wire current?
Modul order number?
Check the polarity of the connected device.
Modul order number?
omar zedan
Dear All
First of all "Thank you for helping"
the second thing what can I say???????? I Connect the jumper "in analog module" in B position instead of D position and I thoght I put it in D position