[?]: S7 317-2DP CPU going to Stop Mode
arun_ikon
Post by arun_ikon »
We are facing the problem in S7 317-2DP CPU, its going to stop mode.
PLC ARRANGEMENT
Rack 0
Slot 1-Power supply Slot 2-CPU Slot 3-IM Slot4-11-DI Cards (321-1BH02-0AA)
Rack1
Slot 3-IM Slot 4-10-DO Cards (322-1HF02-0AA0) Slot11-AI (331-7KF02-0AB0)
Rack2
Slot 3-IM Slot4-6-AI Cards Slot7 -9-AO Cards (332-5HF00-0AB0)
We are slave system we are running the plc either hardwired or profibus according to selection. We have six Pumps starting fro master plc. If we start one by one upto 5 pumps are running if we start any pump in last (i.e. sixth) CPU Going to stop Mode with 5 min. We have Changed All analog card and including CPU its going to stop mode. For Your information we have downloaded OB121, OB122 Block also but it is still going to stop mode. Set point for valve we were getting from master plc.
Finally we have changed analog input (set point to valve) in the rack 1 Slot 4(Replaced from Slot11) it was run for six hours then same problem came. What could be reason?
Diagnostic buffer of module CPU 317-2 DP
Order No./ Description        	Component                     	Version
6ES7 317-2AJ10-0AB0           	Hardware                      	5
- - -                         	Firmware                      	V 2.6.5
Boot Loader                   	Firmware expansion            	A 10.13.9
Rack:                         	0
Slot:                         	2
Event 1 of 100:  Event ID 16# 4548
STOP caused by I/O management
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
07:32:53.457 AM  06/15/1994
Event 2 of 100:  Event ID 16# 2943
I/O access error, writing
P area, word access, Access address:    568
Requested OB: I/O access error OB (OB122)
Priority class:  1
External error, Incoming event
Event 3 of 100:  Event ID 16# 2943
P area, word access, Access address:    566
Priority class:  1
Event 4 of 100:  Event ID 16# 2943
P area, word access, Access address:    564
Priority class:  1
07:32:53.456 AM  06/15/1994
Event 5 of 100:  Event ID 16# 2943
P area, word access, Access address:    562
Priority class:  1
Event 6 of 100:  Event ID 16# 2943
P area, word access, Access address:    560
Priority class:  1
07:32:53.455 AM  06/15/1994
Event 7 of 100:  Event ID 16# 2943
P area, word access, Access address:    594
Priority class:  1
07:32:53.452 AM  06/15/1994
Event 8 of 100:  Event ID 16# 2943
P area, word access, Access address:    590
Priority class:  1
07:32:53.451 AM  06/15/1994
Event 9 of 100:  Event ID 16# 2943
P area, word access, Access address:    586
Priority class:  1
Event 10 of 100:  Event ID 16# 2943
P area, word access, Access address:    582
Priority class:  1
Event 11 of 100:  Event ID 16# 2943
P area, word access, Access address:    578
Priority class:  1
Event 12 of 100:  Event ID 16# 2943
P area, word access, Access address:    592
Priority class:  1
07:32:53.450 AM  06/15/1994
Event 13 of 100:  Event ID 16# 2943
P area, word access, Access address:    588
Priority class:  1
Thanks and Regards
Arun
Re: [?]: S7 317-2DP CPU going to Stop Mode
Need screencopy of your HWConfig with adress of modules
P area, word access, Access address:    ***
PQW 5** is AO module.
Check HW Config adress, module mounting...
arun_ikon
Post by arun_ikon »
Please see the below link which will display HW config Sceen Shot with address.
We have checked Config Address and mounting Everthing seems to be OK.
Error is showing analog ouput only.
Give some ideas to solve the issue.