I have a cpu 224 ac/dc/rly and a temperature to frequency converter 0-265 hz.
Anibody can explayn how to read the temeperature of pt 100?
THANKS
[?]: Pulse reading temeperature of pt 100 ?
dorofteius
venix
Hello!
You need a calibrator device.Look at Adjustment of Measurement Range and Zero Point (Offset) in the following link.Your converter is not calibrated.
[dead] :/229683071/A ... verter.pdf
If you don't need precise measurement then for 1 degree Celsius you have a value of 2 ... 2.5(Rule of 3 - Regula de 3 simpla
Best regards!
Venix
Best regards!
Venix
dorofteius
Already did-it whith the rule of thre
The problem is that it goes whith an error.
At 40 I have 100 degrees, and at 11 it goes at 25.
And I still need 1 degree resolution because it is nicer
not that I realy need-it.
And btw, the rapid share link is not working, and i have already readed the datasheet of the converter, and this model can't be calibrated.
Whith the switces You can just cange the input tipe (tested by me )
Thanx for your help. ( din ce oras esti? ).
venix
Hello!
You can use a potentiometer connected in series with PT100 to increase the scale.You set the potentiometer for 100 degree Celsius to have 265Hz.The potentiometer must be linear with a value of 100 ohms(as far precise as possible).When you got it you can measure the resistance of the potentiometer and change with a/some resistors at the same resistance.
The potentiometer and the resistors are temperature dependant so try to put in an constant temperature(away from the transducer).
Hope this will help!
Best regards!
Venix
Best regards!
Venix