I have a siemens cpu 226 and i want to coonect it to a cpu 414 of siemens with profibus ,
is it possible to connect them without EM277?
I cant find the GSD file for CPU 226, can anyone help me?
thanks
[?]: Connecting S7 CPU 226 to CPU 414 with Profibus
Re: [?]: Connecting S7 CPU 226 to CPU 414 with Profibus
Hellojoopiter wrote:Dear friends
I have a siemens cpu 226 and i want to coonect it to a cpu 414 of siemens with profibus ,
is it possible to connect them without EM277?
I cant find the GSD file for CPU 226, can anyone help me?
thanks
You already understood without Em277 it's not possible to establish Profibus connection. S7-200 can only be profibus slave. If you have EM277 look at How can you communicate data between the S7-200 and the S7-300 via PROFIBUS DP? ( http://support.automation.siemens.com/W ... en/2615830 ). In this link you'll find GSD file for EM277.
Other possibility-connection via MPI, look at http://support.automation.siemens.com/WW/view/en/747743 , but this type of connection has some restrictions, be careful.
Hope this helps
regards