[?]: How to select screen in ProTool using Plc Job 51?
venix
Post by venix »
Hi! Can someone tell me how to select screen using plc job 51 in protool?For example,if a memory bit is set I want to call a function wich shall do Select screen job 51.My PLC is C7-633.I set up Interface Area on DB 11,and I made this data block also in Step 7 Blocks.I create a function like in the documentation :
OPN DB 52 (in C7-633 is CALL in place of OPN but this is wrong I think because it appears in red)
L  9
T DBW 6
L 5
T DBW 8
L 1
T DBW10
L 51
T DBW4
Even so,I get the red SF Led and my CPU is going in Stop mode.
Best regards!
Re: [?]: How to select screen in ProTool using Plc Job 51?
what logic between DB11 & DB52????
post your diagnostic buffer with information about stop or apload your full programm on file-exchanger for analise
venix
Post by venix »
I put the diagnosis buffer below.The code for FC 3 is:
OPN DB 11
L 1
T DBB 6
L 9
T DBB 7
L 0
T DBB 8
L 6
T DBB 9
L 0
T DBB 10
L 1
T DBB11
L 51
T DBB 5
THE DIAGNOSTIC BUFFER :
Diagnostic buffer of module C7 CPU 633/P
Order No./ Description Component Version
6ES7 633-1DF02-0AE3 Hardware 1
- - - Firmware V 1.2.0
Rack: 0
Slot: 2
Event 1 of 100:  Event ID 16# 4562
STOP caused by programming error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class:    1
FC number:      3
Module address:      6
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
11:09:42.959 AM  05/06/2008
Event 2 of 100:  Event ID 16# 2523
Area length error when writing
Global DB, byte access, Access address:      6
Requested OB: Programming error OB (OB121)
OB not found, or disabled, or cannot be started in the in the current operating mode
Event 3 of 100:  Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
11:04:09.437 AM  05/06/2008
Global DB, byte access, Access address :6
your DB not have DBB6...
you need open DB & add DBB6...DBB11
venix
Post by venix »
Thank you Sania for your reply!
I hope it will work
