reymond_craig
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
Post
by reymond_craig » Wed Sep 26, 2007 3:48 am
Good morning, I just want to ask for some help on how to gather data on other s7300 cpu w/out using cp.
Is it posible to get using profibus DP only?
Do I need some Standard FC? Please, your help will be much appreciated.
Thank you very much in advance.
![Smile :)](./images/smilies/icon_smile.gif)
-
lonzo
- Posts: 46
- Joined: Tue Oct 03, 2006 7:09 am
- Location: Europe
Post
by lonzo » Thu Sep 27, 2007 2:45 pm
-
reymond_craig
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
Post
by reymond_craig » Fri Sep 28, 2007 5:11 am
Hi Sir,
Thanks for the useful links. This will help me to improve my knowledge on siemens automation system.
Thank you very much.
Warm regards,
Rey
-
PrackeR
- Posts: 3
- Joined: Mon Oct 30, 2006 5:48 pm
- Location: Netherlands
Post
by PrackeR » Tue Oct 02, 2007 4:44 pm
Hello,
You can use sfc14 and sfc15 to transfer consistent data via profibus to/from another cpu.
One cpu will be the master the other slave.
I'm using it very often to transfer a lot of data.
regards,
PrackeR
-
reymond_craig
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
Post
by reymond_craig » Thu Oct 04, 2007 2:45 am
Hello,
Thanks Pracker, I think I should try this too. It looks interesting. By the way, if I'm going to transfer many data does it means that I need to repeat to call this sfc's in my ladder editor, because i think it only transfer 1 byte per call. And I can't undrstand that much what should I put on the parameter LADDR? If you don't mind Can I have snapshot on where you get this address when you program this? I think I 'm taking some of your precious time but your help will make me a better one in my chosen field. Thank you.
Thank you very much.
Warm regards,
Rey