[?): why PLCSIM V14 forces data to HMI?

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
Post Reply
m_eijie
Posts: 3
Joined: Fri Apr 21, 2017 6:41 am

[?): why PLCSIM V14 forces data to HMI?

Post by m_eijie » Fri Apr 21, 2017 6:45 am

hi
i have a problem with plcsim and HMI simulation.
i made a simple start/stop program in TIA V14 and simulated it in plcsim,works fine.
also a simple wincc project created with tag management and some button that indicates start/stop and motor output state.
when i start plcsim and hmi simulation at one time, values [like bit state] that are in plcsim forces to hmi and when i clicked a start button in hmi, nothing run
but when i set start bit in plcsim, output activated and indicators in hmi blinks on.
what is problem in my project?

thanks for yours attention.

CoMod
Site Admin
Posts: 3969
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: [?): why PLCSIM V14 forces data to HMI?

Post by CoMod » Fri Apr 21, 2017 6:50 am

ScreenCopy or YouTube video with problem ?

m_eijie
Posts: 3
Joined: Fri Apr 21, 2017 6:41 am

Re: [?): why PLCSIM V14 forces data to HMI?

Post by m_eijie » Fri Apr 21, 2017 12:45 pm

i cant take video,because this is my office system and i don't have this access. i can upload hole tia V14 project in upload center , if this help to solve my problem i do it.
thanks

CoMod
Site Admin
Posts: 3969
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: [?): why PLCSIM V14 forces data to HMI?

Post by CoMod » Fri Apr 21, 2017 1:28 pm

only screencopy can help

Enrico999
Posts: 2
Joined: Mon Aug 23, 2010 6:32 pm

Re: [?): why PLCSIM V14 forces data to HMI?

Post by Enrico999 » Sat Apr 22, 2017 5:03 pm

Use "Compile Software (rebuild all)" for your HMI and try again

m_eijie
Posts: 3
Joined: Fri Apr 21, 2017 6:41 am

Re: [?): why PLCSIM V14 forces data to HMI?

Post by m_eijie » Tue Apr 25, 2017 5:52 pm

thank you much. my problem solved.i've changed I/O bits status like I0.0 from HMI side, so that's wrong. i must set or reset a memory bit like m0.0 from hmi for start or restart a motor output.

Post Reply