[?]: PC Software CPU 1505s/1507s

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
pedro4321
Posts: 2
Joined: Mon Feb 29, 2016 9:38 pm

[?]: PC Software CPU 1505s/1507s

Post by pedro4321 » Sat Apr 09, 2016 6:24 am

Hello everyone.
Can some one point mi to the installation media of CPU 1507s?
i'd like to test it.

Beavis
Posts: 14
Joined: Tue Dec 16, 2008 1:28 pm
Location: Asia

Re: [REQUEST] CPU 1507s: Me too!

Post by Beavis » Thu Apr 14, 2016 11:47 am

The product code is SIMATIC SOFTWARE CONTROLLER CPU 1507S DL (6ES7672-7AC00-0YG0)
If anyone has it, please upload it! (tyou)

CoMod
Site Admin
Posts: 3582
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

CPU 1507s =1505S

Post by CoMod » Thu Apr 14, 2016 8:29 pm

about https://support.industry.siemens.com/cs ... controller
link https://support.industry.siemens.com/cs ... ti=0&dl=en
CPU 1505S - PREINSTALLED ON ET 200SP OPEN CONTROLLER
6ES7672-5AC00-0YA0
SIMATIC S7-1500 SOFTWARE CTRL CPU 1505S
SIMATIC S7-1500 SOFTWARE CONTROLLER CPU 1505S VERSION 1, SINGLE LICENSE F. 1 INSTALL, R-SW, CLASS A, 6 LANGUAGES: GE,EN,IT,FR,SP,CH;
PREINSTALLED ON ET 200SP OPEN CONTROLLER
1507S ON DVD SIMATIC_CPU1505S_V1.8.1.iso (589,2 MB)
6ES7672-7AC00-0YA0
SIMATIC SOFTWARE CONTROLLER CPU 1507S
SIMATIC S7-1500, SOFTWARE CONTROLLER CPU 1507S VERSION 1.8, SINGLE LICENSE F. 1 INSTALL, R-SW, SW AND DOCU.
ON DVD, LICENSE KEY ON USB STICK, RT-SW CLASS A, 6 LANGUAGES (GE,EN,FR,IT,SP,CN) EXECUTABLE UNDER WINDOWS 7 REFERENCE-HW: SIMATIC IPC4X7D, IPC6X7D, IPC8X7D
For install on PC it required 2 partions on disk
https://support.industry.siemens.com/cs ... -cpu-1507s
SIMATIC S7-1500 Software Controller Additional Information on CPU 1505S/CPU 1507S
Creation of the CPU volume
Introduction
The CPU makes use of the mass storage of the PC on which it is installed. During the installation, a discrete CPU volume is
created in the mass storage, in which all CPU data is stored. The load and retentive memories are integrated into this CPU
volume.
Note
Size of the CPU volume
In order to ensure reliable operation of the CPU, the CPU volume must not be reduced during operation. If you reduce the
assigned mass storage area, this can lead to data loss or even a CPU crash.

capsute
Posts: 40
Joined: Wed Sep 12, 2007 2:44 am
Location: China

Re: [REQUEST] CPU 1507s

Post by capsute » Sun May 01, 2016 1:12 pm

is it possible to intall SIMATIC_CPU1505S_V1.8.1.iso (589,2 MB) on a normal PC?
IF YES,HOW?

capsute
Posts: 40
Joined: Wed Sep 12, 2007 2:44 am
Location: China

Re: [REQUEST] CPU 1507s

Post by capsute » Wed May 04, 2016 6:13 am

After installing the SIMATIC_CPU1505S_V1.8.1 on normal pc,I got a error screen saying fatal error unsupported pc type,how to solve this problem.

pedro4321
Posts: 2
Joined: Mon Feb 29, 2016 9:38 pm

Re: [REQUEST] CPU 1507s

Post by pedro4321 » Fri May 06, 2016 6:37 am

Yes, correct. thats what happen with 1505S. I was successful removing that alarm modifying the bios in a virtual machine but after that i got another cpu error message.
Thats why i was looking for the 1507S iso.

capsute
Posts: 40
Joined: Wed Sep 12, 2007 2:44 am
Location: China

Re: [?]: PC Software CPU 1505s/1507s

Post by capsute » Fri May 06, 2016 9:18 am

If you get it,and eventually make it run on normal pc,don't keep it.

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [REQUEST] CPU 1507s

Post by yanzixiang » Sat Aug 20, 2016 3:01 pm

pedro4321 wrote:Yes, correct. thats what happen with 1505S. I was successful removing that alarm modifying the bios in a virtual machine but after that i got another cpu error message.
Thats why i was looking for the 1507S iso.
can u share the method how to modify ths bios in the virtual machine ?

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Mon Aug 29, 2016 8:15 pm

I uploaded 1507S here: viewtopic.php?f=30&t=24416

Please share your method for modifying the virtual machine bios

hardprogger
Posts: 8
Joined: Thu Dec 01, 2011 4:18 pm

Re: [REQUEST] CPU 1507s

Post by hardprogger » Fri Sep 23, 2016 6:50 am

I'm also searching for a method to run the controller on vmware.

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Sun Oct 02, 2016 12:27 pm

Windoze wrote:I uploaded 1507S here: viewtopic.php?f=30&t=24416

Please share your method for modifying the virtual machine bios
if we want to modify the bios of the vm,
we need the bios information of a running IPC which 1507 runs on,
use the tool

http://gnuwin32.sourceforge.net/packages/dmidecode.htm

to dump the bios,

then ........

Image

can u have a simens IPC which runs 1507 software CPU?

if u have, can u use hexedit to dump the CPU volume to a file?

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Mon Oct 03, 2016 10:29 am

Sorry, I don't have access to a compatible Siemens IPC...

Info
Faq & Info
Faq & Info
Posts: 414
Joined: Wed Oct 05, 2005 9:00 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Info » Mon Oct 03, 2016 5:06 pm

(sdoc) Delivery Release for SIMATIC S7-1500 Software Controller V2.0
https://support.industry.siemens.com/cs ... ti=0&dl=en

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Tue Oct 04, 2016 1:00 am

Windoze wrote:Sorry, I don't have access to a compatible Siemens IPC...
Image
Microbox PC IPC427D
Box PCs IPC227E, IPC627D and IPC827D,
Panel PCs IPC277E,IPC477D and IPC677D
Rack PCs IPC647D and IPC847D

the cheapest one may be IPC227E.
at this URL,
https://support.industry.siemens.com/cs ... 0&lc=en-DE

we can download the Latest BIOS file,
can u upload the file?

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Tue Oct 04, 2016 1:34 pm

The smallest one supported seems to be the SIMATIC IPC427D.
I have uploaded the latest bios for it here:
https://mega.nz/#!0ZcHkA4D!0w_bt6BTw0XM ... DP17Ssvvk4

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Tue Oct 04, 2016 2:14 pm

thanks a lot!

Image

another error occurs.
i thanks it must be about the CPU volume.

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Tue Oct 04, 2016 2:45 pm

Can you tell me what you have modified in the vmware bios. I want to experiment a bit myself.

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Tue Oct 04, 2016 5:02 pm

I am using VMware so I had to change the DMI strings in the BIOS file.
Before I got the same "Unsupported PC type" now I get a different error:
Image

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Wed Oct 05, 2016 8:27 am

how many cores do you set in the vm?
when i try to set 2 cores in the vm,
i get the error as you post,
after i change it back to 1 core,
my error occurs again.

Windoze
Posts: 12
Joined: Sat Aug 27, 2016 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Windoze » Wed Oct 05, 2016 8:57 am

I only tried 2 and 4 cores.
You need at least 2...
1 core for the cpu, the rest for windows

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Wed Oct 05, 2016 2:16 pm

Image

What does "module +16" mean in Grub4Dos?
What is "{FBBDD621-CB50-491C-986F-F05B42E80B95}"?

Anyone can help ?

vrman
Posts: 1
Joined: Mon Oct 04, 2010 7:24 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by vrman » Thu Oct 06, 2016 7:20 am

Description is here
13.3.25 module
— Command: module file ...

Load a boot module file for a Multiboot format boot image (no interpretation of the file contents are made, so the user of this command must know what the kernel in question expects). The rest of the line is passed as the module command-line, like the kernel command. You must load a Multiboot kernel image before loading any module. See also modulenounzip.

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Fri Oct 07, 2016 2:06 am

that is right,but i already know about it, the manual does NOT talk about "module +16".

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Fri Oct 07, 2016 6:15 am

After modify some parts of the kernel,
I can this error
Image

Left image is the real PC,right image is the virtualbox,
The real PC supports VT-X,but the virtualbox does NOT.
As we can NOT run a virtualbox in a virtualbox,
We can not test 1507 on a virtualbox either.
We must use a real PC.
Image

hardprogger
Posts: 8
Joined: Thu Dec 01, 2011 4:18 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by hardprogger » Fri Oct 07, 2016 9:39 am

yanzixiang wrote:After modify some parts of the kernel....
Which modifications on the kernel have you done? Can you provide some detailed information/files?
I'm playing arround with Vmware and I saw that I have VT-x support inside the virtual machine.
But my problem is, that I have an hardware error on core 0 at startup.
The error with the manufacturer is already fixed.

Beavis
Posts: 14
Joined: Tue Dec 16, 2008 1:28 pm
Location: Asia

Re: [?]: PC Software CPU 1505s/1507s

Post by Beavis » Mon Oct 24, 2016 3:09 pm

Got any progress using a vmware image?
Did you get a working bios? can you share some details
thanks

John

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Thu Oct 27, 2016 11:42 am

some guys asked me what modifications have I did.

I disassembed the kernel,
and guese where to modify,
up to this time,
I failed.

Image
Image

There are so many tests,
and i have no clue.

If we can have one running BOX in touch for test,
maybe we can make it.

I upload the modified kernel files,
if u guys want to test it ,
please backup your vmm.elf and replace it with my vmm.elf.

If u have good luck,
let me know.

链接: https://pan.baidu.com/s/1o8NcVLw 密码: err6

Beavis
Posts: 14
Joined: Tue Dec 16, 2008 1:28 pm
Location: Asia

Re: [?]: PC Software CPU 1505s/1507s

Post by Beavis » Wed Nov 02, 2016 1:54 pm

Hello.
I tried your elf but got no result (fatal error or crash)
I guess you used a custom bios for the virtual machine (otherwise you might get "unsupported pc type").
I used a tweaked version of FUJITSU211_314.ROM (the Bios file I used for WinAC RTX under vmware) and replaced the "vmware" vendor strings with "siemens". With that I got past the "unsupported pc type" but got other faults.

What "bios" file did you use?(under entry "bios440.filename=" inside the vmware .vmx file)

In one of your screenshot i saw an error "vmx disabled"..... that error theoretically can be avoided setting the setting "Virtualize intel VT-x/EPT" setting... did you try that?

bye
john

yanzixiang
Posts: 12
Joined: Sat Apr 20, 2013 7:51 am

Re: [?]: PC Software CPU 1505s/1507s

Post by yanzixiang » Sat Nov 05, 2016 10:02 am

I used a REAL pc box.

I have knows about the setting "Virtualize intel VT-x/EPT" already,
Thanks.

lazik
Posts: 8
Joined: Tue Apr 14, 2009 4:11 pm
Location: Europe

Re: [?]: PC Software CPU 1505s/1507s

Post by lazik » Mon Nov 21, 2016 4:21 pm

Must try with v2.0 ISO. On OpenController eveything works fine.

delege
Posts: 8
Joined: Wed Sep 08, 2010 6:09 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by delege » Fri Nov 25, 2016 7:51 pm

Can someone post the 2.0Iso and a workaround to run it on vmwaRE?

Zonki
Posts: 2
Joined: Fri Oct 21, 2016 6:30 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Zonki » Sun Jan 01, 2017 5:05 pm

could somebody point me to the download of the CPU1507S V2.0, i search already days bu didnt found. I like ti install this and test it. Same like with the Runtime of WinCC V14.
Thanks a lot.

hardprogger
Posts: 8
Joined: Thu Dec 01, 2011 4:18 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by hardprogger » Tue Mar 28, 2017 8:09 am

I'm also searching for the latest CPU1507S V2.0 ISO image. Is nobody here that can provide the iso?

asdsoft
Posts: 1
Joined: Wed Mar 22, 2017 5:26 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by asdsoft » Mon Apr 10, 2017 4:46 pm


Ernie29
Posts: 1
Joined: Sat Apr 22, 2017 1:58 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by Ernie29 » Sat Apr 22, 2017 2:12 pm

Actually it´s not possible to get it running on "normal" PC.
Tested with V2.0 ISO on "normal" PC (not dedicated SIMATIC BOX PC)

delege
Posts: 8
Joined: Wed Sep 08, 2010 6:09 pm

Re: [?]: PC Software CPU 1505s/1507s

Post by delege » Tue Jul 04, 2017 7:06 am

Hi,
i guess, there are not other news to run this on a non-simatic pc?

hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Mon Oct 02, 2017 12:54 am

https://support.industry.siemens.com/cs ... S_V2_1.exe
https://support.industry.siemens.com/cs ... controller

There is a new version of V2.1, the friend can help download, I can not register Siemens Global Center account, I will express my thanks!

Update
Forum Community
Forum Community
Posts: 351
Joined: Mon Apr 12, 2010 10:59 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Update » Mon Oct 02, 2017 6:45 am


hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Fri Oct 06, 2017 2:39 am

The link I can not open, can help provide other download links? Express thankfulness!

CoMod
Site Admin
Posts: 3582
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: [?]: PC Software CPU 1505s/1507s

Post by CoMod » Tue Oct 10, 2017 5:44 am

hanjinxing wrote:The link I can not open, can help provide other download links? Express thankfulness! (dlink)
install mega plugin to Firefox
Image

hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Thu Oct 26, 2017 8:59 am

Thank you everyone! China is a large local area network, individual rights have been deprived (no)

Link
Forum Community
Forum Community
Posts: 1092
Joined: Fri Oct 20, 2006 9:29 pm
Location: We are anonymous users. We do not read your private messages :( Ask questions in the forum !
Contact:

Re: [?]: PC Software CPU 1505s/1507s

Post by Link » Thu Oct 26, 2017 9:22 am


hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Fri Oct 27, 2017 3:32 am

Thank you very much! The The

hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Wed Nov 29, 2017 1:57 am

Image

capsute
Posts: 40
Joined: Wed Sep 12, 2007 2:44 am
Location: China

Re: [?]: PC Software CPU 1505s/1507s

Post by capsute » Mon Dec 04, 2017 4:07 am

It seems that v2.1 need a new authorization,the latest Sim_EKB_Install have not had it yet?

Update
Forum Community
Forum Community
Posts: 351
Joined: Mon Apr 12, 2010 10:59 am

Re: [?]: PC Software CPU 1505s/1507s

Post by Update » Mon Dec 04, 2017 6:27 am


hanjinxing
Posts: 10
Joined: Mon Oct 02, 2017 12:32 am

Re: [?]: PC Software CPU 1505s/1507s

Post by hanjinxing » Tue Dec 05, 2017 2:58 am

After installing the new license, the same problem

CoMod
Site Admin
Posts: 3582
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia
Contact:

Re: [?]: PC Software CPU 1505s/1507s

Post by CoMod » Tue Dec 05, 2017 5:48 am

Ctrl+Alt+Del is not problem of new key :)

amarillo
Posts: 9
Joined: Wed Dec 27, 2006 6:16 pm
Location: America

Re: [?]: PC Software CPU 1505s/1507s

Post by amarillo » Tue May 22, 2018 1:11 pm

Is this thread dead? No more trying to make it work under VM or regular PC?

Amarillo

Dr.Acrobat
Posts: 44
Joined: Sat Mar 10, 2007 8:11 am
Location: Spain

Re: [?]: PC Software CPU 1505s/1507s

Post by Dr.Acrobat » Sat Feb 09, 2019 1:49 pm

News about it ?
Thanks.

Post Reply