Hotfix 3 for WinCC flexible 2008
http://support.automation.siemens.com/W ... n/31796860
Problems resolved and optimization of configuration scenarios with this hotfix:
● The Reset bit is not reliably executed for the following HMI devices:
– OP 73
– OP 73micro
– OP 77A
– TP 177A
– TP 177micro
– Basic Panels
● The opening times for screens on the TP 177A und TP 177micro have increased with
WinCC flexible 2008.
● The hour glass is not shown when changing screens on the TP 177A and TP 177micro
HMI devices. This can result in malfunctions.
● No "Bit" data type tags should be configured in the "R" area on the OP 77A, TP 177A and
Basic Panels with Allen Bradley DF1, because incorrect values may occur.
● Sporadical interrupts of connection with TP 177micro.
Hotfix 2 for WinCC flexible 2008
http://support.automation.siemens.com/W ... n/31796860
http://support.automation.siemens.com/W ... 08_HF2.exe
This hotfix corrects the following problems in the engineering system and optimizes configuration scenarios:
● Instance update of faceplates
Some changes do not require an instance update of faceplates.
● Errors during compilation
Deriving an instance from faceplates with formatted text results in errors during compiling.
● Error with dragging and dropping faceplates from a library
● Problems updating faceplates
Using formatted text in faceplates results in errors when updating these faceplates.
● Using "Undo" and "Redo" on faceplates with formatted text and structures results in corruption.
● Errors during STEP 7 synchronization
If you replace a CPU with another that has a different revision level, STEP7
synchronization may not function correctly.
● SIMOTION projects cannot be opened
In some circumstances, HMI projects created with WinCC flexible 2007 cannot be opened in SIMOTION.
● Problems with DEMO mode
No DEMO mode after removing valid compact keys.
● Error installing MSDE
● Error message when closing WinCC flexible
If the last action you perform in WinCC flexible is changing the visibility of layers, an error message appears when you close WinCC flexible.
● Canceling "Save as version"
Depending on the computer load, "Save as version" cancels without results.
● Save as version without administrator rights
If you do configuration work without administrator rights, you cannot use "Save as version".
● Internal error
If you delete a trend display that contains routing tags, internal errors occur.
● Illegal array lengths with TP177 6" and TP177 6" portrait devices
● USB PPI cable 6ES7901-3DB30-0XA0 as of Version 06
The "Reset to default settings" fails with the following HMI devices:
– Mobile Panel 277
– MP 277
– Mobile Panel 177 DP
– Mobile Panel 177 PN
– Mobile Panel 277
– TP 177B (without TP 177B 4")
– OP 177B
– TP 277
– OP 277
– MP 177
– TP170A
– TP170micro
This hotfix corrects the following problems in Runtime and optimizes its performance:
● After stopping Runtime and restarting the device, the last language to which you switched is no longer active.
You have transferred a project to an HMI device and switched to a different configured language.
You then stop Runtime and restart the HMI device.
When the HMI device has started and is ready to operate, the language to which you last switched is no longer active.
All CE devices are affected
● After WinCC flexible Runtime 2008 has been removed, some ActiveX applications (for example, Automation License Manager) may no longer run correctly.
Note
It is imperative that the hotfix be installed before WinCC flexible Runtime 2008 is removed.
● Text fields are displayed truncated.
When you convert projects from WinCC flexible 2007 to WinCC flexible 2008, configured text fields may be shown truncated in Runtime, if the "Adapt utomatically" option is disabled
It is obligatory if you want use examples from official site.
Problems resolved and optimization of configuration scenarios with this hotfix:
● Error converting project.
If you convert a project from a previous version to WinCC flexible 2008, the conversion
may fail.
● Defective faceplates after project conversion.
If you convert a project from a previous version to WinCC flexible 2008, individual
faceplates may be defective after project conversion.