[?]: OP17, upload COM problem, have only USB-serial adapter.

ProTool, WinCC flexible, WinCC, PP/OP/TP/TD/MP
jamrobe
Posts: 34
Joined: Sun Dec 02, 2007 2:29 pm
Location: America

[?]: OP17, upload COM problem, have only USB-serial adapter.

Post by jamrobe » Wed May 07, 2008 7:56 am

Hi everybody.

Need to upload a OP17 siemens panel.

Tried with ProSave but it would not accept Com5, only Com1 or Com2.
ProTool accepts other coms, but when I want to back-up it starts ProSave etcetc.

I will try to get a Serial Port Mapper to map Com5 over Com1, however, any other suggestions?

Thanks
Jam

sania
Site Admin
Posts: 1371
Joined: Sat Aug 13, 2005 6:15 am

Post by sania » Wed May 07, 2008 9:35 am

go to device manager & find who use com-port 1 or 2
change number from 1 to any non used
go to your com-port & change

saugarm
Posts: 3
Joined: Sun Apr 27, 2008 4:53 pm
Location: Europe

Post by saugarm » Wed May 07, 2008 2:28 pm

Hello,
you can try this for to find your comport

http://plcforum.uz.ua//SetCOM.exe

jamrobe
Posts: 34
Joined: Sun Dec 02, 2007 2:29 pm
Location: America

Problem solved

Post by jamrobe » Thu May 08, 2008 9:52 am

Thanks for help.

sania : good advice :), the only problem on the beginning I couldn't find port settings for my USB adapter, but after reinstalling the driver from original cd all went ok.

saugarm: thanks for utility, good to have it.

Regards
Jam