[?] how wincc conect to cpu Allen-Bradley

Post by kambiz » Wed Aug 29, 2012 8:58 am

Dear all
how i can conect cpu Allen-Bradley to wincc ?
thanks

bilbo_321
Posts: 87
Joined: Wed May 19, 2010 2:22 pm
Location: Bulgaria

Re: [?] how wincc conect to cpu Allen-Bradley

Post by bilbo_321 » Wed Aug 29, 2012 2:17 pm

Better go to fortune teller.

What kind of PLC?
What communication?
What version of WinCC?

You will get correct answer when you provide more details.

kambiz
Posts: 120
Joined: Sat Dec 09, 2006 5:04 am
Location: Iran

Re: [?] how wincc conect to cpu Allen-Bradley

Post by kambiz » Wed Aug 29, 2012 6:09 pm

1-Allen Bradley SLC 500 PLC System
2-comunication profibus or Ethernet or any Possible
3- wincc 6 or 7
Thanks

bilbo_321
Posts: 87
Joined: Wed May 19, 2010 2:22 pm
Location: Bulgaria

Re: [?] how wincc conect to cpu Allen-Bradley

Post by bilbo_321 » Thu Aug 30, 2012 7:29 am

I think the Ethernet is preffered communication in this case. It is my personal oppinion of course.

You have two options in general:
1. Using RSLinx as OPC Server and WinCC as OPC client;
2. Using built-in communication driver "Allen Bradley - Ethernet IP" in WinCC v.7;

If you are planning to use old WinCC v.6 you have third option: Using RSLinx as DDE Server and WinCC as DDE client. Not very stable and is not recommended. The DDE channel is not supported in WinCC v.7 SP2 and newer.

Using RSLinx gives you more flexibility in communication. You could use any communication supported by PLC. It acts like communication gateway between PLC and SCADA.

My recommendation is to use Ethernet communication and "Allen Bradley - Ethernet IP" driver in WinCC.

Good luck.