Good day! The object often goes out of power and turns off the controller. Is there a system variable in the Schneider that indicates that the controller has resumed its operation, or there was a power supply. At the start of the controller you need to do certain actions.
Thak you.


Top
 Profile  
 
PostPosted: Sat Nov 04, 2017 12:01 am 
Site Admin

Joined: Wed Sep 06, 2006 3:03 pm
Posts: 1097
Location: CIS
Have you checked the manual?

Image
IsFirstMastColdCycle: Indicate if this Cycle is the First MAST Cold Start Cycle
This function returns TRUE during the first MAST cycle after a cold start (first cycle after download or reset cold).

Image
IsFirstMastCycle: Indicate if this Cycle is the First MAST Cycle
This function returns TRUE during the first MAST cycle after a start.

Image
IsFirstMastWarmCycle: Indicate if this Cycle is the First MAST Warm Start Cycle
This function returns TRUE during the first MAST cycle after a warm start.


Top
 Profile  
 
PostPosted: Mon Nov 06, 2017 11:09 pm 

Joined: Fri Nov 03, 2017 9:11 pm
Posts: 2
Thank you!


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC + 3 hours


Who is online

Users browsing this forum: Google [Bot] and 12 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by International PLCforum® Forum Software © PLCforum
Mobile version