Hi all, I newbi on Schneider PLC
I need a wiring schematic download / upload TSX Quantum cpu 113/30
1. Is it possible to directly use the rs 232 serial cable direct to pc / laptop?
2. In Which port for program upload / download on this cpu? Modbus or Modbus Plus?
3. Are there any specific setting in order to Connect? Exp. Baudrate, parity or data bits?
4. Can I use Proworx? NXT or Proworx32?
Thank for your assistance all
[?+]: PLC TSX Quantum CPU 113/30
Re: Need Help..PLC TSX Quantum CPU 113/30
Hello Dear,
The link contains the details of 140CPU11303 http://www.filesonic.com/file/130217547 ... inouts.pdf
on the last two pages you can find the connection diagram.
1. Yes, you can download program via RS232 port of you laptop/PC.
2. You can download program via both ModBus & ModBus Plus port, but for ModBus plus you need ModBus Plus card. It is better you download program via ModBus Port, although it is a bit slow, but it does not required additional hardware to download.
3. The Software automatically scan the ModBus address, baud rate & parity, you don't need to configure it.
4. Yes, You can you ProWorx Software.
BR
Leo-Ali
The link contains the details of 140CPU11303 http://www.filesonic.com/file/130217547 ... inouts.pdf
on the last two pages you can find the connection diagram.
1. Yes, you can download program via RS232 port of you laptop/PC.
2. You can download program via both ModBus & ModBus Plus port, but for ModBus plus you need ModBus Plus card. It is better you download program via ModBus Port, although it is a bit slow, but it does not required additional hardware to download.
3. The Software automatically scan the ModBus address, baud rate & parity, you don't need to configure it.
4. Yes, You can you ProWorx Software.
BR
Leo-Ali
Re: [?]: PLC TSX Quantum CPU 113/30
Yup,
Your answer all is working and I've tried it
Thank you profusely
Case closed
Your answer all is working and I've tried it
Thank you profusely
Case closed