[?]: RTU and Quantum PLC... using Modbus/TCP IP

другие контроллеры
Post Reply
macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

[?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms » Mon Oct 05, 2009 7:36 pm

Hello..please help me on how to communicate an RTU and the Quantum PLC..
My Quantum PLC is the Master and the RTU is Slave.Help me on how to communicate using Modbus/TCPIP protocol... :( :( :(

RomanR
Posts: 48
Joined: Mon Apr 07, 2008 6:18 am
Location: Israel

Post by RomanR » Wed Oct 07, 2009 12:09 pm

Hi macros
1.you softwer for Quantum(modsoft/concept/unity)?
2.need module NOE for TCP/Ip communicate
if you hahve that'is slot namber of NOE
3. you need interaptet communite or all time communicate?

macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

Post by macroms » Wed Oct 07, 2009 2:37 pm

My software is Unity Pro XL. Yes I have already NOE module attached and my RTU is made by Bristol which is Control Wave Micro. My problem is how to read the data from RTU to my Quantum PLC because I want to know the value of the transmitter connected from RTU. Quantum is the Master and the RTU is the Slave.
Sir the slot number of NOE is 5 and the TCP/IP address of the RTU is 192.168.10.20 and my TCP/IP address of Quantum is 192.168.10.1
Please help me how to configure this so that it will communicate each other. :cry:

RomanR
Posts: 48
Joined: Mon Apr 07, 2008 6:18 am
Location: Israel

Post by RomanR » Thu Oct 08, 2009 12:12 pm

Image

macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms » Fri Oct 16, 2009 10:11 am

Sir I have problem I cannot get the data I have no data received in the Quantum PLC and in the Status there is no Error code it is zero so no problem with the blocks..
And also the communication is okey I can Ping the IP address and also I tried to used the Modscan32 and I can see all the data there but in the PLC nothing.
Help please??
Image
Image
Image

RomanR
Posts: 48
Joined: Mon Apr 07, 2008 6:18 am
Location: Israel

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by RomanR » Fri Oct 16, 2009 3:23 pm

ok
1.) chenge Map_Idx from "0" to "1" (Eqw device Id in modskan)
2.) redy jast holding register (40xxxx)

macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms » Sun Oct 18, 2009 5:01 am

Sir I change the Map_index from 0 to 1 but still I cannot read the data from RTU..
And in the Status there is an Error Code 4001 and according to the list of error codes in Unity Pro tells that "Inconsistent response by Modbus slave".
I included the screenshots of my logic for more details.

Image

Image

nightrain
Posts: 1
Joined: Fri Sep 11, 2009 3:35 pm

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by nightrain » Sun Oct 18, 2009 7:35 am

Sir I change the Map_index from 0 to 1 but still I cannot read the data from RTU..
And in the Status there is an Error Code 4001 and according to the list of error codes in Unity Pro tells that "Inconsistent response by Modbus slave".

macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms » Tue Oct 20, 2009 5:18 pm

Image
Image

RomanR
Posts: 48
Joined: Mon Apr 07, 2008 6:18 am
Location: Israel

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by RomanR » Tue Oct 20, 2009 7:26 pm

hi macroms
meby this help to you

1.)change No_Reg from 16 to 32 becose in Modscan you read 32 registers
2.)
macroms wrote:Sir the slot number of NOE is 5 and the TCP/IP address of the RTU is 192.168.10.20 and my TCP/IP address of Quantum is 192.168.10.1
but in you program addres of rtu 192.168.10.21
3.)if you chenge Map_idx from 1 to 0 and you dont have Error code but not data check in this stage if you can chenge same date in distenashen area in Quantum. if you can't chenge(old value retern) is ok you jast read from slave zero date
4.)I'm think is not critikal but chenge Reg_Read to namber of Register thith out deckloreshin eq. %MWxxx
5.)if you can to send me you full program for check

macroms
Posts: 57
Joined: Sat Mar 28, 2009 8:48 pm
Location: Saudi Arabia

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms » Tue Oct 20, 2009 8:09 pm

Sir because we have two RTU's one is 192.168.10.20 and the other is 192.168.10.21 and this two RTU is another vendor and mine only here is the Quantum PLC but my client wants me to communicate with the RTU so that they can also monitor and control the RTU. I also tried to change the number of register from 16 t 32 and it is same.

macroms1
Posts: 5
Joined: Wed Oct 21, 2009 7:19 pm

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms1 » Mon Nov 02, 2009 1:11 pm

Anybody here can help my problem?

I am facing problem communicating the Quantum PLC (Master) and Bristol Bobcock RTU (Slave). The situation is likethis;
1. The polling of data from Quantum PLC(Master) to Slave simulation device (Modsim32) and vice versa are OK.
2. The polling of data from RTU (Slave) to Master simulation device (Modscan32) and vice versa are also OK.
3. But when both Quantum PLC (Master) and Bristol Bobcock RTU (Slave) are connected we cannot poll the data.

Help please... :( :( :(

genjua
Posts: 3
Joined: Fri Nov 06, 2009 9:41 am

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by genjua » Fri Nov 06, 2009 10:49 am

Hello!

well at the CREAD_REG block put 04200 insteat of 200 at SLAVEREG input.
now u must know the address of RTU's as u mention that you have two RTU's....

for example set the address of first rtu = 2 and second rtu = 3

keep that in mind that the address of you plc is 1 make sure that the address of PLC is 1.
one more thing you have 2 rtu's so you have to use 2 tcp/ip blocks and 2 cread_reg blocks

one tcp/ip block with map_idx = 2 and and the other with map_idx = 3 as i mention in the above example......

i hope that this will help you
regards
GENJUA
chk this.....

macroms1
Posts: 5
Joined: Wed Oct 21, 2009 7:19 pm

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by macroms1 » Sat Nov 07, 2009 1:50 pm

Sir I am using Unity Pro for my programming software. So is it Ok sir if will change the SLAVEREG for example 04200 instead of 200?Because in the help of this CREAD_REG block it is stated there that if you want to read 40001 register you will only put 1.

genjua
Posts: 3
Joined: Fri Nov 06, 2009 9:41 am

Re: [?]: RTU and Quantum PLC... using Modbus/TCP IP

Post by genjua » Mon Nov 16, 2009 6:23 am

ya i know abt the help....

but practical is practical do try it!

Regards

GENJUA