CPU S7-300 ELECTRICAL CONNECTIONS

Questions about Siemens & Analog Siemens hardware.
Software & hardware exchanger
Post Reply
cduriez
Posts: 1
Joined: Tue Apr 02, 2013 5:17 pm

CPU S7-300 ELECTRICAL CONNECTIONS

Post by cduriez » Thu Jul 03, 2014 3:53 pm

Presently, I´m working on a project where electrical connections of the PLC are the most important topic due to people safety inside the project. What I need to know is: which electrical cord you think is the apropiate for connect a power supply of 12V with a CPU S7-313C and some additional modules such as SM335. I have worked with AWG 12 and there was no problems but it was just an experiment.

Please send any feedback or idea that you consider helpful.

Regards.

Sliwkoland
Posts: 1
Joined: Fri Jun 27, 2014 4:45 pm

Re: CPU S7-300 ELECTRICAL CONNECTIONS

Post by Sliwkoland » Wed Oct 29, 2014 9:25 pm

Hello.
As I red Your post, my first answer is RTFM...
But.
The basics...
Folowing the safety rules...
You should have two connections, one is for the CPU and HMI , I usually use 1mm square ( something simmilar to AWG 17 ) and it's usually enough . Second for output and relays which should be turned on and off by safety relay ( notaus... ) .
The diameter of the second supply You should count depending on power consumption of the system , wiring lenth and enviromental conditions.
For fast calculations we usually use the the multipier 7Amps/mm square , if we suppouse the enviroment themperature higher than standard or wire lenth more than 100meters we change the multiplier.

12 V for s7 CPU ??
USA version ??