I want to connect a potentiometer to 331-7KF02 card, but I can not find the link, I would possibly be like that as a voltage signal ohms, just to experiment with a plc are a beginner and do not know how
Thank you in advance for any information


Top
 Profile  
 
PostPosted: Thu Aug 19, 2010 3:48 pm 

Joined: Fri Mar 03, 2006 1:18 pm
Posts: 74
Location: Europe
first of all check the jumpers in your card and put them at the right position,then in the hardware configuration in step7 you have also check your settings about mA or Volts signals and then you connect the cables to the terminals 2 (+)&3(-).Then if all are ok you gone see that your piw??? when you are online and rotate your potesnsiometer that change value.hope that helps :evil:


Top
 Profile  
 
PostPosted: Thu Aug 19, 2010 4:29 pm 

Joined: Sun Mar 28, 2010 11:35 am
Posts: 28
I set to "0 .. 10V" on board, but I can not directly connect a potentiometer (test already done) I have to connect a voltage of 10Vdc or 24VDC (in my case) but do not know the value of the potentiometer and connect it


Top
 Profile  
 
PostPosted: Thu Aug 19, 2010 4:49 pm 
Forum Community
Forum Community

Joined: Mon Apr 12, 2010 1:59 pm
Posts: 334
How do you connect a potentiometer to the analog module 6ES7 331-1KF0*-0AB0?
http://support.automation.siemens.com/WW/view/en/17071108
Quote:
You can connect a potentiometer to the analog module 6ES7 331-1KF0.-0AB0 as follows.

* Connect the potentiometer pick-off to terminal M+ of the channel concerned.
* Connect a terminal point of the potentiometer to terminal M- of the input channel.
* Then terminals S- and M- of the connected channel are connected to each other.

Image
Fig. 1: Potentiometer connection for resistance measuring

Notes:

* You can connect potentiometers of up to 6 KOhms.
* If a variable input voltage is supposed to be formed with the potentiometer, the potentiometer pick-up must be connected to U+ and the M side of the potentiometer to M- of the module.

More information is available in the manual "SIMATIC S7-300 Programmable Controller Module Specifications " in Entry ID http://support.automation.siemens.com/WW/view/en/8859629


Top
 Profile  
 
PostPosted: Thu Aug 19, 2010 10:06 pm 

Joined: Sun Mar 28, 2010 11:35 am
Posts: 28
I am grateful for the aid but fails, is not the same card I have now resolved as a resistance connecting pin 2+4 and pin 3+5 with maximum resistance of 600 ohms


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC + 3 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by International PLCforum® Forum Software © PLCforum
Mobile version