plcforum.uz.ua

International PLC Forum
It is currently Sun Apr 22, 2018 9:35 pm

All times are UTC + 3 hours




Post new topic Reply to topic  [ 3 posts ] 
Author Message
PostPosted: Wed Mar 29, 2017 7:34 am 

Joined: Wed Aug 10, 2011 3:25 pm
Posts: 3
Hi

I am involved in a project consisting S7-315 2DP, 3 ET200M, 5 ACS800, 8 ACS550, and WinCC station as a PLC commisioner and programmer. Which are all connected through Profibus.

ABB drives are equipped with RPBA-01. Design of the electrical cabins are in a way that drives are powered up with a contactor by PLC and then starts whenever is needed by Profibus.

The problem is when RPBA-01 powers up PLC goes to stop mode. So, contactor switches off and drive powers down as a result. I managed to use external power for RMIO in ACS800 drives, and ACS800's problem is solved. RPBA-01 in ACS800 drives is always powered on and there is no fault on PLC, but still when ACS550 drives are powered up PLC goes to stop mode. I would be grateful if anyone could guide me or recommend a solution for this problem.

I should mention the settings in ABB drives are correct. If drive's powering up contactor is bypassed, the first time RPBA-01 powers up there will be a fault in the PLC, but when PLC's fault is reset everything works prefect. Problem arises when RPBA-01 powers up during PLC's run mode, if RPBA-01 powers up before PLC starts there will be no problem.

I appreciate your kind response in advance.

Regards
Mojtaba Azarnoosh


Top
 Profile  
 
PostPosted: Thu Mar 30, 2017 5:01 pm 

Joined: Tue Oct 08, 2013 2:14 pm
Posts: 3
I think you need to try using diagnostic OB in the STEP 7 program.


Top
 Profile  
 
PostPosted: Fri Mar 31, 2017 11:44 am 

Joined: Wed Aug 10, 2011 3:25 pm
Posts: 3
haziev123 wrote:
I think you need to try using diagnostic OB in the STEP 7 program.


Thanks for your response.
Unfortunately I'm not at the site right now.
I'll try as soon as possible.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC + 3 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by International PLCforum® Forum Software © PLCforum
Mobile version