Hi all
how i can replace posidrive fas4000 with ls is5 ? plc s7300 315-2DP and control with profibus DP
befor posidrive work with plc after damage how i can replace with is5 ? possible or no ?
[?] posidrive replace with ls is5
Re: [?] posidrive replace with ls is5
Hello:for your question you must check if:
1-in your old drive in profibus they used PPO3.
2-ls is5 have profibus option (GSD FILE) and you must change hardware configuration in simatic manager .
then you can replace it without change in program other wise you need to change in program.
1-in your old drive in profibus they used PPO3.
2-ls is5 have profibus option (GSD FILE) and you must change hardware configuration in simatic manager .
then you can replace it without change in program other wise you need to change in program.
Re: [?] posidrive replace with ls is5
tnx for answer
only chang HWconfig Enough ?
program dont need chang ?
only chang HWconfig Enough ?
program dont need chang ?