[?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Tue Nov 17, 2009 12:45 pm
by ciwa
Dear All,
Anyone have experience with connecting Micromaster 440 using PC Adapter via RS485 port?
is it possible?

Regards,
Ciwa

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Wed Nov 18, 2009 4:11 pm
by kriztof
If you want to connect inverter to PC it's easy. Micromasters have RS485 interface as I remember correctly there are two blue connectors 29(Data+) and 30(Data-), just attach your adapter to these connectors and use DriveMonitor.

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Fri Nov 20, 2009 6:07 am
by ciwa
hi kriztof,

i tried but no luck. are there parameter should be set??

regards,
Ciwa

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Fri Nov 20, 2009 6:21 pm
by kriztof
i tried but no luck. are there parameter should be set??
Yes, you have to configure USS protocol parameters, use parameter range: P2009 – r2037
Operating instruction:
http://support.automation.siemens.com/W ... ype=133300
Parameter list:
http://support.automation.siemens.com/W ... reeLang=en

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Sat Nov 21, 2009 10:55 am
by ciwa
hi kriztof,

the parameter already set, but still no luck. I use Starter and set the PG/PC interface as PC Adapter(PPI) is this correct?

The cable schema

PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
8 ---------------- 29 ---- Data A
3 ---------------- 30 ---- Data B

When I try to connect the MPI & USB light are blinking but no device found. :(

Regards,
Ciwa

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Sun Nov 22, 2009 7:42 am
by kriztof
I use Starter and set the PG/PC interface as PC Adapter(PPI)
I thought it's only for S7 200 connection? Do you mean Simatic PC Adapter for S7? Sorry I didn't understand you correctly.
I use RS232-RS485 converter and DriveMonitor, it works with Micromaster, Simovert, Simoreg.

Re: [?]: Connecting MM440 using PC Adapter via RS485 port?

Posted: Wed May 03, 2017 4:17 pm
by thai_truong
ciwa wrote:hi kriztof,

the parameter already set, but still no luck. I use Starter and set the PG/PC interface as PC Adapter(PPI) is this correct?

The cable schema

PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
8 ---------------- 29 ---- Data A
3 ---------------- 30 ---- Data B

When I try to connect the MPI & USB light are blinking but no device found. :(

Regards,
Ciwa
Hi guy,
I did test successfully by connecting STARTER (PC) to Micromaster MM440 via terminal 29, 30 (RS485 port) using USB-RS232-PPI/RS485 cable, but the wiring should be follow:

PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
3 ---------------- 29 ---- TRX+
8 ---------------- 30 ---- TRX-