Hello,
Can someone tell me what are the outputs of Dixell xjp60d on Modbus RTU?
Ia have to connect 12 of them on a Deltav 12.3.
I found
https://www.yumpu.com/en/document/view/ ... ll-devices
and i have
manual http://www.emersonclimate.com/europe/Pr ... P30D_E.pdf
but i can not link one to another.
My question is: the parameters described in manual at page 2/4 section 9(list of parameters) and at page 4/4 ( section 16 general parameters and section parameters) are somewhere in modbus list of xjp60d?
All i can understand from general modbus manual is that i can find probe values at registers 256,257,258,259,260,261 (valid for the first 3 probes-read only so this is input register), and at register 2816,2817,2818,2819 are real time clock (read write) so that will be holding register.
Where are the remaining 3 probes values? It will be the registers 262,263,264,265,266,267?
If i setup up the registers 256,257,258,259,260,261 as holding register would i read anything?
And where is the slave address of device? Is it at register 1 and 2 included in device code?
Thank you.
Interlink emrson 12.3 deltav and dixell xjp60d devices
-
- Posts: 15
- Joined: Fri Aug 07, 2009 6:21 am
- Location: Romania
Re: Interlink emrson 12.3 deltav and dixell xjp60d devices
Hi
if you have problem with DeltaV system, you can ask in Emerson forum
http://www.emersonexchange365.com/opera ... ge/deltav/
if you have problem with DeltaV system, you can ask in Emerson forum
http://www.emersonexchange365.com/opera ... ge/deltav/