Hello all,

has anyone else had an issue trying to right click configure devices from the rswho screen and it be stuck on configure remote devices via linx gateway for that specified driver?

I've tried this for DF1 driver and 1784-U2DHP driver yet it still pops up with this tcp driver even though I'm not using and its not in the configure drivers screen.
Under communications > Configure Gateway I have enable RSLinx Classic Gateway unchecked.

When I try to use rlogix500 and goto comms > whos active go online > and select my driver to see whose active on the dh+ network it says the same configuring the settings to a linx gateway is not allowed. add a new tcp driver ("remote devices via linx gateway") in rslinx classic and then select your path through the driver.

never had this happen before I updated to 2.59, tried 2.57 and 2.58 but the issue is still there.

thanks for any help


Top
 Profile  
 
PostPosted: Fri Jun 02, 2017 5:00 am 

Joined: Mon Mar 13, 2017 10:15 am
Posts: 3
Figured it out if anyone else has this problem, delete the 2 harmony files for rslinx.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC + 3 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by International PLCforum® Forum Software © PLCforum
Mobile version