Changing SLC 5/02 to SLC 5/05

RSLinx, RSLogix, RSView, LogixPro ...
rahulmm7
Posts: 7
Joined: Wed Dec 10, 2014 6:11 am

Changing SLC 5/02 to SLC 5/05

Post by rahulmm7 » Mon Feb 08, 2016 9:58 pm

Hello

We need to change 1747-L524 processor to 1747-L552 without interrupting the on-going process.Is there any way to do that,and i hope there is no redundancy module for SLC processors..Please help me as am in the critical stage.

PCNightmare
Posts: 4
Joined: Thu Feb 07, 2013 8:21 am

Re: Changing SLC 5/02 to SLC 5/05

Post by PCNightmare » Tue Mar 01, 2016 7:08 am

You will need to shut the process down, best you can do is have the new processor loaded with the project ready to go to keep downtime to minimum.