[?]: How download program from CJ1M PLC ?

CX-One, CX programmer, NTST, Syswin ....
nguyenthe_k
Posts: 11
Joined: Sun May 11, 2008 11:14 am
Location: Vietnam

[?]: How download program from CJ1M PLC ?

Post by nguyenthe_k » Sun May 11, 2008 11:29 am

(( Hi, I'm newbie to PLC world. So please don't laugh at my stupid question. :oops: )


I am trying to connect to a CJ1M CPU21 but the PLC seems does not detect my cable connection - RS232C. These conditions have been virified by me:

The CPU setup (CJ1M CPU21) is correct.
The connecting method is Toolbus.
The com port is correct ( in this case, I set the cable port to COM1)
The 5th dip switch in the PLC was on.

When I first pluged in my cable, the COMM indicator was light up, but if I tried to connect to PLC, it switched to off.


The cable I am using has been vefified and connected successfully to the other PLC (CQ1M...), but not the series CJ1M ???

In my case, do I fortget something important ??

most
Posts: 431
Joined: Sat Oct 22, 2005 7:17 am
Location: Europe

Post by most » Thu May 15, 2008 9:45 pm

CJ1M, it never passed for my hands but I give a small help with manuals.
http://www.idom.ru/files/Omron/FA/Manuals/Plc's/

read 340, ..., 345, 380 and 336
the cable for CQM is not for CJ. i think
if to obtain what you intend says some thing because also I am interested for the future. :wink:
best regards

nguyenthe_k
Posts: 11
Joined: Sun May 11, 2008 11:14 am
Location: Vietnam

Post by nguyenthe_k » Mon May 19, 2008 11:16 am

I've found the cable serial diagram of CQM1, anyone has the rest.
http://plcforum.uz.ua//O ... d.zip.html

The CJ1M and CQM1 actually share the same cable diagram. Look at this documentation.
http://plcforum.uz.ua//O ... g.pdf.html

Anyone has the experience with this ?? Please help !

most
Posts: 431
Joined: Sat Oct 22, 2005 7:17 am
Location: Europe

Post by most » Mon May 19, 2008 1:59 pm

you did not look very well ...

this is the cable (if it is equal to CQM, ...I did not compare ...)
Image

with switch 4 and 5 tries on off ....
Image

with cx programmer chooses "Auto Online" or the "Sismac Way" in manual.
search with google this manual "W393_E1_07_CJ1_Operation_Manual.pdf" +- 12 Mb
this pdf have all that you need.
edit
http://plcforum.uz.ua//W ... l.rar.html

your cable is for HMI Proface (if it is equal ...i did not compare...)

regards

Husanto
Posts: 21
Joined: Mon Jun 30, 2008 2:32 am
Location: Indonesia

Connect PLC CJ1M

Post by Husanto » Fri Nov 28, 2008 4:26 am

You can try with this :
1. Turn On the dip switch pin 5
2. Set in your CX - programmer with default setting, baudrate 19200
3. check u Comm port, it must same with auto detect in your PC COMM
4. Using sysmac way Communication
5. Try to connect again.

Hope this help...

Husanto