TIA portal RunTime can not connect to PLC.

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
Lexiy
Posts: 9
Joined: Tue May 25, 2010 3:47 am

TIA portal RunTime can not connect to PLC.

Post by Lexiy » Tue Apr 27, 2021 2:44 pm

Hi All.
I have strange situation. TIA portal v15. Project with PLC and SCADA on Runtime professional.
I can connect to PLC with "go online", but if i start Runtime then no conection to PLC. Another PC with same TIA Portal can connect to PLC via "go online" and Runtime.
On PC with problem is installed Windows 10 prof, Wirewall off. PLC with IP on the local network.
I try to disable antivirus. It is not solve problem.

I readed manuals. TIA portal use port 102 for all conections. Is it correct or "go online" and RunTime are use different ports?
Can anyone help me? Any ideas? 12 years with Siemens PLC and the first time such a problem.

a12sdd
Posts: 5
Joined: Sun Apr 25, 2010 2:22 am

Re: TIA portal RunTime can not connect to PLC.

Post by a12sdd » Tue Apr 27, 2021 3:24 pm

Use Wireshark to filter what is happened between your PC and PLC.

Best Regards

sender
Posts: 2
Joined: Mon Nov 08, 2010 7:16 am

Re: TIA portal RunTime can not connect to PLC.

Post by sender » Fri Apr 30, 2021 11:51 am

Set ALSO the S7 interface from Set PG/PC Interface (old settings for Simatic Manager).
Sounds crazy but Runtime uses also settings from Set PG/PC Interface.

waynejonstone
Posts: 6
Joined: Thu Apr 18, 2013 9:53 am

Re: TIA portal RunTime can not connect to PLC.

Post by waynejonstone » Sat May 01, 2021 6:16 pm

check your access point settings of S7ONLINE.
https://support.industry.siemens.com/cs ... n&lc=de-AT