Post by Вадим » Fri Mar 31, 2006 5:11 pm

Подскажите плз,
возможно ли открыть проект созданный в Step7 пакетом Step7Lite?

Possible open Step7 project in Step7Lite ?

Guest

Post by Guest » Fri Mar 31, 2006 7:11 pm

With STEP 7 and STEP 7 Lite it is not possible to import the hardware configuration of the other software. You can however make a "detour" via the controller, store the hardware configuration on your CPU and then load it back into the other software using the function "PLC > Load in programming device...". Here you should note that STEP 7 Lite can only read in those modules that can also be configured with STEP 7 Lite.

Note:
Hardware configurations in which

DP configuration has been use, e.g. changing an I slave into a master CPU, or
modules have been replaced and the default addresses of the new module have been changed by accepting the values of the module originally configured,
are displayed as read-only after loading the configuration in STEP 7 Lite, because of the deviations from the default addressing. To be able to use the configuration sections in such cases you must transfer the modules into a new station using copy/paste.