[?]: s7-300 PID temperature control for heat/cool operation
badr3
Post by badr3 » Wed Jul 13, 2011 9:21 am
I'd like to ask a question,
is there a PID function block for heat/cool operation for s7-300
Best regards.
dsekulic
Re: [?]: s7-300 PID temperature control for heat/cool operat
Post by dsekulic » Wed Jul 13, 2011 11:51 pm
Try function blocks FB58 (Continuous Temperature Controller "TCONT_CP") and FB59 (Temperature Step Controller FB59 "TCONT_S")
Search word(s): pid temperature control
badr3
Post by badr3 » Thu Jul 14, 2011 11:12 am
many thanks for your replay ,
i need a function block with two settings (pid parameters), one for heat and the other for cool.
concerning heat i will use SSR for heats , and for cooling i will use relay for blowers
dsekulic
Post by dsekulic » Thu Jul 14, 2011 5:30 pm
I don't know what SSR stand for, but for turning on/off of blower You can use Pulse generator output (take a look pages 25-27). Parameters of PID function block You can find on appendix A.3.
dmitry_79
Post by dmitry_79 » Mon Jul 18, 2011 5:16 am
The Regulator of the cooling differs from regulator of the heating, that that when cooling is used negative factor to propotions.
Excuse me for my english...
dsekulic
Post by dsekulic » Mon Jul 18, 2011 12:23 pm
You can use one PID regulator with mapping of output manipulated value for heating and for cooling. If error is positive than You use mapping for cooling and vice versa.
Scarch
Post by Scarch » Sat Sep 10, 2011 9:33 am
FB59, it is the typical application for an extruder, with heating resistors and cooling fans. I have used it several times.