i use analog input AIW0 from analog module EM235. Signal on the input AIW0 is 0(4) ... 20 mA (0...32000), but that signal is unstable!
-
Coyote
- Posts: 41
- Joined: Wed Sep 06, 2006 10:07 am
- Location: Slovenia
Post
by Coyote » Tue Sep 08, 2009 10:59 am
So, what's up. You should make the signal stable, there is no other way. You can also apply filter for analog signals (see the system block).
-
dsekulic
- Posts: 186
- Joined: Sun Feb 12, 2006 5:47 pm
- Location: Europe
Post
by dsekulic » Tue Sep 08, 2009 3:12 pm
Hi,
Maybe You have some interference in vicinity of measuring system. Do You You use screened cable?
regards
-
xdoit
- Posts: 35
- Joined: Wed Nov 21, 2007 2:13 pm
- Location: China
Post
by xdoit » Sat Sep 19, 2009 2:01 pm
hi,
You should use STP (Shielded Twisted Pair) cable for that sensor and make sure only one end to be connect to earth.
rgds,