[?]: PCS7 V7.0 SP2 and WIN SERVER2003 / XP PRO

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
Post Reply
NimaMoaddeli
Posts: 4
Joined: Wed Mar 25, 2009 7:20 am
Location: Iran

[?]: PCS7 V7.0 SP2 and WIN SERVER2003 / XP PRO

Post by NimaMoaddeli » Sat May 23, 2009 7:30 am

DAER FRIENDS,

I'M TRYING TO COMMISSIONS PLANT USING PCS7 V7.0 SP2 MY PROBLEM IS AS FOLLOW,I WILL APPRECIATE IF SOMEBODY HELP ME URGENTLY

I have one es with win xp pro and 2 OS-server with Server2003 and one cas with Server2003 istalled.
I'm trying to make workgroup for them so i have changed all all the workgroup "simatic-wg" and i named
my PCs AS ES="SIMATIC-ES"/OS SERVER1="SIMATIC-OSS1"/OS SERVER2="SIMATIC-OSS2"/CAS="SIMATIC-CAS1"/OS-CLIENT1-10="SIMATIC-OSC1"/"SIMATIC-OSC2",......
I also set their ip as following ES=192.168.1.21/OSS1=192.168.1.22/OSS2=192.168.1.23/CAS1=192.168.1.24/OSC1(OS CLIENT1-10)=192.168.1.25-35

Also for all of them I set login username and password as follow= username:Administrator Password:(No Password)

With SIMATIC-Shell I can See all PC and With Networkplace I' able to see them
but I cannot share folder in OS-Servers to download the OS on them
However with PCS7 I'm able to configure both OS Server Form ES
and I can Download Station Setting in OS Servers but I'm not able to download whole OS (WINCC Application) and As I said I'm not able to access to a computer from other even when I share a folder,
My firewall is Also off
and I did run the program called "simatic security" to do the security setting required but i'm not able yet

Moreover when I try to download OS (WINCC APPLICATION) from ES it says "unable to reach station"

So Please Help me urgently

DLEU
Posts: 1
Joined: Thu May 07, 2009 6:04 am
Location: Europe

Problem to dowload OSs

Post by DLEU » Wed May 27, 2009 4:37 pm

Hello,

here some tips :
1. u should define a not blank password for the administrator account, and set it the same on all computers (cause of windows Policy),
2. If u rename the computers, check that the name of the station in Station configurator is the right one. Else correct it and download the HwConfig of each stations.
3. Set the PG/PC interface configuration on "PC Internal"
4. In u're project (on ES = Engineer Station) open each OS (WinCC) and check that the computer name is the one of the ES (in "Computer" Folder of WinCC, on the right)
5. Check the target folder of the OS's in the SIMATIC Manager...

If it does'nt help u reply... Good Luck

Leopard
Posts: 24
Joined: Sat Nov 28, 2009 3:31 pm

Re: [?]: PCS7 V7.0 SP2 and WIN SERVER2003 / XP PRO

Post by Leopard » Wed Mar 09, 2011 3:57 pm

Hi
Is there any training pdf for whole PCS7 commissioning Workstation.If true plz share it.
Is there any PCS7 system exists with Domain?

Post Reply