[?]: How change the value of FM350-2 COUNTER

Post by zajabbar » Tue Apr 21, 2009 1:35 pm

Hello all.
I have a FM350-2 and reading count value good
i need to change the value of each counter .

can help pls
best regards

weijah
Posts: 21
Joined: Wed Mar 22, 2006 8:51 am
Location: Europe

Post by weijah » Wed Apr 22, 2009 7:05 pm

i dont understand .what do you want to change ?

zajabbar
Posts: 4
Joined: Sun Oct 26, 2008 9:48 am
Location: Saudi Arabia

Post by zajabbar » Thu Apr 23, 2009 6:21 am

as you know FM 350-2 can read from 8 encoders and when the cpu of the plc turn off for any reason all counters will be 0
thats whay i need to reload xxxx value for each counters .


best regards

weijah
Posts: 21
Joined: Wed Mar 22, 2006 8:51 am
Location: Europe

Post by weijah » Thu Apr 23, 2009 8:48 am

i never this function before.but i read the manual for the fm350-2 and you can use the fc cnt2_wr ( fc 3 ) from the biblothek fm_cntli.with this fc you can write values to every channel of the counter card.