Re: Control Schneider Sepam S40 via Modbus RTU

I found a solution. In order to use TC1 and TC2 "Circuit breaker control" function have to be activated.
Thanks for the help!
Best regards!
by dimovqq
Thu Nov 10, 2016 12:41 pm
Forum: Industrial network
Topic: Control Schneider Sepam S40 via Modbus RTU
Replies: 3
Views: 9651

Re: Control Schneider Sepam S40 via Modbus RTU

Yes, I am using SFT2841 but I don't think TCs can be configured to triger outputs, LEDs or something else. I think that they are meant to do a specific action and nothing more. On page 117 from the manual there is block diagram, which explains on which conditions binary output O1 should be triggered...
by dimovqq
Wed Nov 09, 2016 11:21 am
Forum: Industrial network
Topic: Control Schneider Sepam S40 via Modbus RTU
Replies: 3
Views: 9651

Control Schneider Sepam S40 via Modbus RTU

Hello, I have the following problem: when I send TC1 Tripping (command bit for activating tripping) binary output O1 does not close and nothing happens. In the manual for the S40 is written that this is possible. I am successfully switching setting groups and resetting, so I don't think this is comm...