Re: ControlNET problem

Thank you for your help. The problem was solved, it was in the optical cable. More precisely in the connector. The attenuation in the normal range, but through a microscope - seen strong contamination. Well, that was found specialist equipment at the facility.

P.S.Topik can be closed.
by zer-gut
Wed Jul 29, 2015 4:51 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: ControlNET problem
Replies: 5
Views: 3744

Re: ControlNET problem

Да, проблема оказалась в оптическом кабеле, точнее в коннекторах, они были грязные. (Приехал специалист и с помощью специального оборудования подтвердил и почистил их)
by zer-gut
Mon Jul 27, 2015 5:07 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: ControlNET problem
Replies: 5
Views: 3744

Re: ControlNET problem

Спасибо. Система новая. Изначально ПЛК был версией 20.55, столкнулись с проблемой и заказчик попросил прошить на 19.53, так как все контроллеры на объекте 19 версии. Прошу прощения , модуля EN2T/D версии 10.007. Нет, я не использую блоки ALMA и ALMD вообще. Сегодня обнаружили интересную вещь, по одн...
by zer-gut
Sun Jul 26, 2015 5:38 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: ControlNET problem
Replies: 5
Views: 3744

ControlNET problem

Добрый день. Надеюсь моя тема не останется от ответа. Опишу ситуацию: Есть резервированная система. Удаленные шасси подключены по оптике. RSNetWorx сконфигурирован согласно проекта (длина кабелей + модуля повторители). Периодически происходит сбой сети, в результате потеря узла(ов) сети. В диагности...