Search found 69 matches

by bilbo_321
Sun Jun 10, 2018 9:41 am
Forum: SIMATIC system
Topic: [?]: Connect S7-1500 PLC with Allen Bradley
Replies: 3
Views: 4729

Re: [?]: Connect S7-1500 PLC with Allen Bradley

I assume your ControlLogix has got Ethernet comms module. You can connect PLCs without any extra hardware like gateways. Both PLCs support Open TCP or UDP communication and you can exchange data. Even a very large block of data. It is a bit more complicated, compared to using gateway, because you ne...
by bilbo_321
Sun Apr 26, 2015 10:27 am
Forum: SIMATIC system
Topic: Object oriented programming on StructuredText in S7
Replies: 2
Views: 5440

Re: Object oriented programming on StructuredText in S7

This is what I can answer to your questions: 1) Full support IEC 61131-3 related to object oriented programming (properties, inheritance, polymorphism, interfaces, ets): Yes, Step7 and TIA Portal conforms to IEC 61131-3, but it is NOT object oriented programming. Classic IEC 61131-3 standard doesn't...
by bilbo_321
Sun Mar 01, 2015 9:26 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: [REQUEST]Softlogix 5 Anyone has it?
Replies: 6
Views: 4864

Re: [REQUEST]Softlogix 5 Anyone has it?

What version do you need?
I've got version 2.1 and 2.1.1 and I could upload it to Mega.
This version runs on WindowsNT4 SP6 or Windows2000 SP3 as I remember.
Let me know if you need it.
by bilbo_321
Thu Jan 01, 2015 10:18 am
Forum: SIMATIC system
Topic: Question about PN data reading
Replies: 6
Views: 3915

Re: Question about PN data reading

You have to set-up TCP port 102 in your router. Siemens PLCs use port 102 for TCP communication. Check Siemens support web site, there are few documents and guides how to set-up router for TCP communication.
by bilbo_321
Mon Oct 21, 2013 12:32 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: How set data/time in processor
Replies: 1
Views: 1922

Re: How set data/time in processor

Use SSV Instruction with ClassName "WallClockTime".
by bilbo_321
Fri Aug 30, 2013 12:05 pm
Forum: Simatic (Russian)
Topic: И опять PID регулятор
Replies: 5
Views: 4942

Re: И опять PID регулятор

No, it isn't exe. You have to scroll down on download page, not just click on first link on top.
Check this http://fake/how-to-use-wwwhot ... t=hotfiles how to download from http://www.hotfiles.ro.
by bilbo_321
Mon Aug 12, 2013 8:09 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?]: Activation of Studio 5000 Logix
Replies: 41
Views: 133138

Re: Activation of Studio 5000 Logix

"The controller you requested contains firmware revision 1.03. logix designer support for this revision is not installed." but i installed all from the studio 5000. can you help me with that to. Firmware 1.03 is the basic firmware. New PLC is delivered from factory with this firmware and you have t...
by bilbo_321
Thu Aug 01, 2013 8:29 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Communicating PLCs via ControlNet and EtherNet/IP
Replies: 6
Views: 5047

Re: Communicating PLCs via ControlNet and EtherNet/IP

RSLinx is for communication to AB PLCs only. It doesn't support S7 protocol. The equivalent communication software for S7 PLCs is Simatic Net. Go to Siemens support site and search for it. The free alternative to Simatic Net is LibNoDave http://libnodave.sourceforge.net/ , but it involves programming.
by bilbo_321
Tue Jul 30, 2013 9:35 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Communicating PLCs via ControlNet and EtherNet/IP
Replies: 6
Views: 5047

Re: Communicating PLCs via ControlNet and EtherNet/IP

You can use RSLinx Classic. It is Communication software from AB used for communication to any AB PLC. It has built- in OPC server, but unfortunately it is not available in free "RSLinx Lite" version. You have to get license for Single node, OEM or Gateway version. Check this link: https://rockwella...
by bilbo_321
Fri Apr 12, 2013 7:44 am
Forum: Simatic (Russian)
Topic: Взлом пароля S7-315F
Replies: 10
Views: 15916

Re: Взлом пароля S7-315F

Search for pss7.
Here is the link: viewtopic.php?f=1&t=17844&p=57434&hilit=pss7#p57434
by bilbo_321
Thu Apr 04, 2013 8:59 am
Forum: SIMATIC system
Topic: [?]: Replace a 315-2PN/DP CPU
Replies: 5
Views: 3921

Re: [?]: Replace a 315-2PN/DP CPU

Sorry, my mistake. You are right.
It could be a problem if you upload program from one PLC (MMC) and load it on different.
It is OK if you just swap MMCs.
by bilbo_321
Wed Apr 03, 2013 4:31 pm
Forum: SIMATIC system
Topic: [?]: Replace a 315-2PN/DP CPU
Replies: 5
Views: 3921

Re: [?]: Replace a 315-2PN/DP CPU

You can do it if you swap only PLCs, without changing IO modules or remote IOs . S7-300 has no load memory and uses MMC as such load memory. All the logic and configuration is stored ONLY on MMC card, so if you plug MMC2 into PLC1 it will act as PLC2. You don't need to do any changes in NetPro or HW...
by bilbo_321
Fri Mar 29, 2013 3:54 pm
Forum: Simatic (Russian)
Topic: [?]: Проблемы при изменении конфигурации
Replies: 10
Views: 8204

Re: [?]: Проблемы при изменении конфигурации

I don't think GSD file is the problem. It is just description of Profibus DP module prorerties. All the information for communication to DP slaves is in System data (SDBs) of DP master. Look carefully in diagnostic buffer of PLC or save and post it here. There should be information about which FB or...
by bilbo_321
Sat Mar 23, 2013 10:52 am
Forum: Simatic (Russian)
Topic: [?+]: Проблема при подключении CP5711 к PLC в DP порт
Replies: 9
Views: 6639

Re: [?]: Проблема при подключении CP5711 к PLC в DP порт

Could be what CoMod said, but do the following: 1. First check Profibus DP address of CP5711. It MUST be unique and not duplicate with any of the master or slave DP addresses! 2. Remove PG/PC is the only master on the bus in Set PG/PC Interface. 3. Check Profibus network speed ant other network sett...
by bilbo_321
Wed Mar 13, 2013 6:58 pm
Forum: Other PLC
Topic: [LINK]: Modsim32 license
Replies: 7
Views: 6273

Re: [LINK]: Modsim32 license

Sorry,
Fixed sharing, so it should be OK now.
by bilbo_321
Wed Mar 13, 2013 11:59 am
Forum: Other PLC
Topic: Honeywell Touch screen
Replies: 2
Views: 1727

Re: Honeywell Touch screen

(pgood) Thanks for sharing your experience.
by bilbo_321
Fri Jan 18, 2013 6:41 pm
Forum: Simatic (Russian)
Topic: [?]: Кол-во коммутационных связей CPU 317F-2 PN/DP
Replies: 2
Views: 2827

Re: [?]: Кол-во коммутационных связей CPU 317F-2 PN/DP

Hi, In the manual "S7-300 CPU 31xC and CPU 31x: Technical specifications" http://cache.automation.siemens.com/dnl/Tk/Tk1MDQwMQAA_12996906_HB/s7300_cpu_31xc_and_cpu_31x_manual_en-US_en-US.pdf you can see: " Allocating connections by means of programming In S7 basic communication and in open Industria...
by bilbo_321
Fri Nov 09, 2012 10:11 am
Forum: SIMATIC system
Topic: [?]: S7 Steam heated tank PID control
Replies: 1
Views: 12696

Re: [?]: S7 Steam heated tank PID control

Hi, At first I am not an expert in PID Control, but I've used it for many years and many tasks. I will give you my personal opinion and answers to your questions. 1. Question about the valve – each valve has its own response characteristics. Yes, you should try to make it as linear as possible. Mayb...
by bilbo_321
Thu Aug 30, 2012 7:29 am
Forum: SIMATIC HMI
Topic: [?] how wincc conect to cpu Allen-Bradley
Replies: 3
Views: 5653

Re: [?] how wincc conect to cpu Allen-Bradley

I think the Ethernet is preffered communication in this case. It is my personal oppinion of course. You have two options in general: 1. Using RSLinx as OPC Server and WinCC as OPC client; 2. Using built-in communication driver "Allen Bradley - Ethernet IP" in WinCC v.7; If you are planning to use ol...
by bilbo_321
Wed Aug 29, 2012 2:17 pm
Forum: SIMATIC HMI
Topic: [?] how wincc conect to cpu Allen-Bradley
Replies: 3
Views: 5653

Re: [?] how wincc conect to cpu Allen-Bradley

Better go to fortune teller.

What kind of PLC?
What communication?
What version of WinCC?

You will get correct answer when you provide more details.
by bilbo_321
Thu Jul 19, 2012 4:53 pm
Forum: SIMATIC system
Topic: Need advice about DP-Slaves diagnosis
Replies: 3
Views: 3915

Re: Need advice about DP-Slaves diagnosis

Use SFC51 (RDSYSST) with SZL_ID=W#16#00B3 or SZL_ID=W#16#00B4 in OB86 or OB82 or even in OB1. To use it in OB82 you should enable diagnostic interrupt of DP slaves. Be careful: SFC51 is processed asynchonously. The exeption is when you call it in OB82 with SZL_ID=W#16#00B3 and it is processed immedi...
by bilbo_321
Thu Jul 05, 2012 10:53 am
Forum: Simatic (Russian)
Topic: Вызов функционального блока с индексированным вызовом экземп
Replies: 3
Views: 5597

Re: Вызов функционального блока с индексированным вызовом эк

You could put "// входные преобразования word_0 := WORD_TO_BLOCK_DB (INT_TO_WORD (index*100)).DBW0; word_1 := WORD_TO_BLOCK_DB (INT_TO_WORD (index*100)).DBW2; word_2 := WORD_TO_BLOCK_DB (INT_TO_WORD (index*100)).DBW4; " and "//выходные преобразования WORD_TO_BLOCK_DB (INT_TO_WORD (index*100)).DBW0 :...
by bilbo_321
Wed Jul 04, 2012 11:28 am
Forum: Simatic (Russian)
Topic: [?] Как убедиться в "незанятости" I адреса и Q адреса?
Replies: 5
Views: 5835

Re: [?] Как убедиться в "незанятости" I адреса и Q адреса?

With SFC14 and SFC15 you can read/ write consistent data larger than 4 bytes.
Maybe it is better to use SFC14/15 for drive control and status feedback.
by bilbo_321
Mon Jul 02, 2012 10:18 am
Forum: Simatic (Russian)
Topic: Вызов функционального блока с индексированным вызовом экземп
Replies: 3
Views: 5597

Re: Вызов функционального блока с индексированным вызовом эк

Hi Balagur, You can't call FB with index of instance DB as I know. You can try to define UDT with structure of your DB and then create a DB with array of that UDT. later in OB1 or FC you can call your FB in a cycle with I/O variable of the same UDT type. See the code below. //=================== TYP...
by bilbo_321
Fri Jun 22, 2012 5:09 pm
Forum: Simatic (Russian)
Topic: Внешнее питание на PC Adapter USB для MPI и Profibus
Replies: 13
Views: 19844

Re: PC не видит Adapter USB (6ES7972-0CB20-0XA0)

Да, попробовал. Работает без проблема.
by bilbo_321
Thu Jun 21, 2012 1:43 pm
Forum: Simatic HMI (Russian)
Topic: [?] Поле Статус в Alarm View
Replies: 1
Views: 4244

Re: [?] Поле Статус в Alarm View

If you acknowledge alarm in a mean time (before it gets back to false) you will see only "D" in status column.
"CD" in status means alarm was true and then false without acknowledge.
by bilbo_321
Tue Dec 20, 2011 7:55 pm
Forum: SIMATIC system
Topic: [?]: Communicating STEP7 with SIPROTEC by ProfiBus
Replies: 3
Views: 3494

Re: [?]: Communicating STEP7 with SIPROTEC by ProfiBus

I had a similar problem few years ago. The difference was the communication. I used Profibus FMS. For that I had to have the DIGSI project to import in Step7 project. From few protection relays I couldn’t read certain parameters. The problem was that I had no the latest DIGSI project (another compan...
by bilbo_321
Fri Nov 18, 2011 9:39 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?] Barcode reader and 1769-L35E CompactLogix
Replies: 12
Views: 11927

Re: [?] Barcode reader and 1769-L35E CompactLogix

I am glad to help you.
That's the idea of this forum, to exchange knowledge and hepl each other.

Good luck!
by bilbo_321
Thu Nov 17, 2011 12:28 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?] Barcode reader and 1769-L35E CompactLogix
Replies: 12
Views: 11927

Re: [?] Barcode reader and 1769-L35E CompactLogix

sample code from SICK web site: https://rapidshare.com/files/4017462229 ... amples.zip
There is a pdf file in archive. It could give answers to your question.
by bilbo_321
Wed Nov 16, 2011 4:42 pm
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?] Barcode reader and 1769-L35E CompactLogix
Replies: 12
Views: 11927

Re: [?] Barcode reader and 1769-L35E CompactLogix

Hi LenPatrick,

did you found the sample code from SICK web site?
I could upload it to Rapidshare if you have any troubles?
by bilbo_321
Sat Nov 05, 2011 7:05 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: [?] Barcode reader and 1769-L35E CompactLogix
Replies: 12
Views: 11927

Re: [?] Barcode reader and 1769-L35E CompactLogix

Please type the exact barcode reader type. There is a range of CLV62x products with different communication options. For example: CLV620-0120 supports CAN, Ethernet TCP/IP, and EtherNet/IP available on board, no additional gateway needed (depending on variant)... There is a sample code at SICK web s...
by bilbo_321
Thu Oct 27, 2011 3:00 pm
Forum: Simatic (Russian)
Topic: [?]: Выбор тензодатчика для весового комплекса
Replies: 4
Views: 4827

Re: Выбор тензодатчика для весового комплекса

Check CAS web site: http://www.globalcas.com/bemarket/shop/index.php?pageurl=page_goodslist&part_code=130005000 I've used few times CAS load cells and I had no problems. And they are cheaper than SIEMENS. Distributor in my country (Bulgaria) is ATARK Ltd http://atark-bg.com/site/page.php?32 Here is ...
by bilbo_321
Fri Oct 21, 2011 9:56 am
Forum: Other Books
Topic: Programmable Logic Controllers (4th Ed) by Frank D Petruzell
Replies: 0
Views: 12005

Re: Programmable Logic Controllers (4th Ed) by Frank D Petru

RAR Archive is password protected. Please provide the password.

10x.
by bilbo_321
Tue Oct 18, 2011 10:40 am
Forum: Simatic HMI (Russian)
Topic: wincc_flex запуск на более чем 1 компе
Replies: 12
Views: 7585

Re: wincc_flex запуск на более чем 1 компе

You can run more than one WinCC flex Runtime at the same time. That's for sure. I've found this FAQ at Siemens Support site https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=28027290&ehbid=23369901&query=S7%2D300+resource&load=treecontent&lang=en&siteid=cseus&aktprim=0&ob...
by bilbo_321
Mon Oct 17, 2011 8:47 am
Forum: Simatic HMI (Russian)
Topic: wincc_flex запуск на более чем 1 компе
Replies: 12
Views: 7585

Re: wincc_flex запуск на более чем 1 компе

Did you tried to increase number of OP connections in HW Config of both PLCs? From the screenshots you've posted I can see that HMI is connecting and disconnecting at all the time. That problem doesn't exist if there is only one HMI running. Correct? What version of WinCC Flexible is there? Any serv...
by bilbo_321
Sat Oct 15, 2011 8:18 am
Forum: Simatic HMI (Russian)
Topic: wincc_flex запуск на более чем 1 компе
Replies: 12
Views: 7585

Re: wincc_flex запуск на более чем 1 компе

Old System could work because SimaticNet OPC Server opens only one connection to PLCs and 3 PCs running VB are OPC clients and fetch data from OPC server, not from PLCs.
by bilbo_321
Sat Oct 15, 2011 7:05 am
Forum: Simatic HMI (Russian)
Topic: wincc_flex запуск на более чем 1 компе
Replies: 12
Views: 7585

Re: wincc_flex запуск на более чем 1 компе

Try to remove "Cyclic operation" check box. Below is the excerpt from the WinCC flex online help concerning this: "When cyclic operation is enabled, the PLC optimizes its data exchange with the HMI device. This increases system performance. Disable cyclic mode if you are operating several HMI device...
by bilbo_321
Wed Oct 12, 2011 11:07 am
Forum: Industrial network
Topic: Does TCP/IP equal ModbusTCP (TCP/IP = ModbusTCP???)
Replies: 8
Views: 22455

Re: Does TCP/IP equal ModbusTCP (TCP/IP = ModbusTCP???)

No, they are completely different things. ModbusTCP is a wrapper of classic Modbus protocol developed for use on Ethernet networks. ModbusTCP uses TCP protocol. They are at different levels in OSI 7- layer model. See https://rapidshare.com/files/2678858939/Modbus_Messaging_Implementation_Guide_V1_0a...
by bilbo_321
Tue Oct 11, 2011 6:59 am
Forum: Allen-Bradley (Rockwell Automation)
Topic: Request: ABCIP protocol
Replies: 3
Views: 2961

Re: ABCIP protocol

That's it. I've been looking for it too. (gpost)
by bilbo_321
Sun Oct 09, 2011 3:33 pm
Forum: SIMATIC system
Topic: [?]: remote touch panel mp277 ?
Replies: 2
Views: 1812

Re: [?]: remote touch panel mp277 ?

Check Sm@rtAccess or Sm@rtService option for wincc flexible.
by bilbo_321
Wed Oct 05, 2011 6:50 am
Forum: SIMATIC system
Topic: [?]: conect Data acquisition modules adam-4019+ to plc 300 ?
Replies: 11
Views: 7464

Re: [?]: conect Data acquisition modules adam-4019+ to plc 3

It sounds like CP configuration is not correct. Maybe it is not configured for ASCII protocol???
Could you check STATUS word of FB for send & receive? post here the hex values if possible.
by bilbo_321
Sun Oct 02, 2011 1:14 pm
Forum: SIMATIC system
Topic: [?]: connection between PC <---> cpu 224
Replies: 11
Views: 6354

Re: [?]: connection between PC <---> cpu 224

use the same MPI cable.
by bilbo_321
Wed Sep 28, 2011 3:05 pm
Forum: SIMATIC system
Topic: [?]: conect Data acquisition modules adam-4019+ to plc 300 ?
Replies: 11
Views: 7464

Re: [?]: conect Data acquisition modules adam-4019+ to plc 3

That's good progress. :) Use command #AAN as i wrote in my first post. I am telling you again: READ THE ADAM MANUAL , chapter 5, page 5-11. Here is the description of command: #AAN Name: Read Analog Input from Channel N command Description: The command will return the input value from one of the eig...
by bilbo_321
Wed Sep 28, 2011 6:37 am
Forum: SIMATIC system
Topic: [?]: conect Data acquisition modules adam-4019+ to plc 300 ?
Replies: 11
Views: 7464

Re: [?]: conect Data acquisition modules adam-4019+ to plc 3

it is not very clear. Could you write down exactly pin-to-pin connection or draw a simple schematic? Keep in mind that ADAM module should be configured with address, using or not check sum, baudrate, etc.. Please read the complete ADAM 4000 manual (especially Chapters 2, 4, 5 and Appendix E). I can'...